Citect scada M340 connection status

the18

Member
Join Date
Nov 2019
Location
Casablanca
Posts
18
Hello,
M340 plc.
3 standalone citect scada applications.
Connection type (OFS server).
Same application on all 3 stations and multiple logins to give access to certain commandes rights.

I was asked to have a network page in which you can check connection health in a diagram with 1plc connected to 3 stations.
My question is how can the plc knows the 3 stations status, i found IODeviceInfo in citect help, but the application is the same and thus we can't talk to the other scadas.
Thank you.
Also how to run cicode functions constantly ?
 
create a heartbeat bit in the plc which constantly switches on and off....the you can monitor it in the scada. Also sure there is a system bit wich will switch off if theres no comms. Just cant remember where
 
Hello, i can't since it is the same application duplicated on 3 stations which means a heartbeat to all three would pinpout at the same variable unless there is a way to choose a tag in runtime.
 

Similar Topics

Hello all, I got a call yesterday from a worker at a factory where i installed an automation sistem with a PLC M340, operated via SCADA Vijeo...
Replies
3
Views
4,807
hello everyone,, i want to communicate citect scada v7.2 with modicon m340 plc via ethernet....i don know where to assign all...
Replies
0
Views
2,893
please what are the steps can i do in vijeo citect to communicate to plc m340 ? with details please ....
Replies
5
Views
4,790
I am trying to display a variable within a cicode function onto a graphics page. This function queries a SQL database. I can get the value onto a...
Replies
3
Views
288
We are trying to set up a newer generation Omron PLC (NX/NS Series) with Citect / Aveva Plant SCADA using the Ethernet/IP CIP Protocol to read...
Replies
2
Views
360
Back
Top Bottom