nagy2011 Member N Join Date Nov 2012 Location giza Posts 23 Nov 2, 2012 #1 please what are the steps can i do in vijeo citect to communicate to plc m340 ? with details please ....
please what are the steps can i do in vijeo citect to communicate to plc m340 ? with details please ....
Chris Taylor Lifetime Supporting Member Join Date Feb 2011 Location Canterbury Posts 257 Nov 2, 2012 #2 You can tell us what you have done already. Chris
nagy2011 Member OP N Join Date Nov 2012 Location giza Posts 23 Nov 2, 2012 #3 http://www.mediafire.com/?llm8f8oh6bdmj3b,3urvygii0i6nrz7,qt967sp593b4hai and in express wizard i choose m340 modbus/tcp and put in it the ip add of plc
http://www.mediafire.com/?llm8f8oh6bdmj3b,3urvygii0i6nrz7,qt967sp593b4hai and in express wizard i choose m340 modbus/tcp and put in it the ip add of plc
Chris Taylor Lifetime Supporting Member Join Date Feb 2011 Location Canterbury Posts 257 Nov 2, 2012 #4 Check your port names
nagy2011 Member OP N Join Date Nov 2012 Location giza Posts 23 Nov 2, 2012 #5 what is the wrong in it
Chris Taylor Lifetime Supporting Member Join Date Feb 2011 Location Canterbury Posts 257 Nov 2, 2012 #6 Your I/O device is looking at Port2board1 and your port is Port1Board1 Perhaps the I/O device should be Port1Board1 What is the set up for the M340?
Your I/O device is looking at Port2board1 and your port is Port1Board1 Perhaps the I/O device should be Port1Board1 What is the set up for the M340?