I've done a few pre and post.
Pre PLC would be Analog drives such as the AB 1336 or whatever the part number was.
Makes no difference to me.
I've used eurotherms, Control Techniques, whatever the customer wanted and was within its budget.
The drive gets an analog signal to ramp up to a point and maintain speed.
Either PLC or a speed pot will do the job.
Since the tach goes to the PLC and fed to the drive I see no issue with signals unless you have had the uncontrolable ramp up before the install.
I used to retro Harris M110, 110Bs, 300s etc.
I've used all kinds of drives and usually ended up using the existing ones as we were doing primarily the controls/PLC upgrades and the things ran forever.
I cannot see how a "bad" motor worked without a hickup with the old drive, then the Eurotherm and now it is acting up.
I'm out of options here.
No alarms, cooling is more than enough (according to you),no changes were made recently besides the new drives(right??), the only things left are analog signals somehow get scrambled and screw up the drive or the drive itself is bad or misconfigured.
Bringing someone in with a megger wouldn't hurt at this point.
A couple of drive experts on here , you may get something that I've missed so far from them if they decide to jump in DickDV & Leifmotif (sorry about any wrong spelling, not intentional).
I think it is time to step back and think about things.
1. This is a 10 year old machine
2. Motor winding temp sensors are set for 40C. They operate because he is getting 43C in the motor.
3. VFD cabinet is now overheating. I am thoroughly confused why maintenance took a heat gun to the VFD cabinet.
4. YOu mentioned 24 / 7 operation and said you run it heavy.
There was no mention of PMs or periodic checks.
OK so he has a motor that is getting warm. He has a VFD that is getting warm. That indicates to me they are fully loaded.
BASICS
Motor will produce the torque demanded by load.
Motor will demand current proportinal to load from VFD
VFD will supply that current within its setup configuranion parameters.
Now then since the machine is 10 years old maybe the problem really comes down to that it is getting old and worn and the total torque demanded is at the upper bound of the motor (thus heating). I would recommend going thru the machine and looking for wear and bad bearings, gearboxes etc. For sure I would check gearbox lubricant levels and lube quality. One of those IR heat detectors may be quite useful in finding bad bearngs and hot spots in drive train.
My bet is your maintenance is only to keep this running. I know how it goes "we'll check that after this order" then the next order gets dumped on and they want it yesterday.
I would install ammeters on AC line supplying drive all three phases. I would consider installing ammeters on both shunt and series field / armature and keep an eye on these currents and voltages while machine is running. This will for sure tell you how heavy you are loading motor. It will also tell you if you need to have shop check out motor.
The "high" speed at startup still bugs me. I wonder if your tach gen is not slipping. I would pull at a MUCH later date and do a bench check of it to ensure RPM is proportional to voltage and double check the drive. Not a problem for now and can wait until later.
Dan Bentler