Hello. We use AB PowerFlex 7000 drives in a pump station. The operator just called to report a fault on one drive:
"STATUS: Faulted"

"FAULT: DI Contactor"
5fwh


We can clear the fault and the motor restarts, but it recurs a few moments later.


I have searched Rockewell's manual with list of fault codes to no avail. Does anyone have any info on what this means? I assume it points to a problem with the Drive Input contactor (see this manual, page 9).


Could this fault be related to the electronic interlocks associated with isolation switch etc? Not sure where to begin diagnosis.


Thanks for any pointers.
 
I believe it is telling you that it is not getting a Digital Input feedback from the line input contactor. That could mean that the contactor is dropping out, or the aux contact is opening or the circuit to it is.
 

Similar Topics

I have 3 new PowerFlex 7000 VFD's. Rockwell was out to do some checking before startup. These are part of a larger electrical project. I gave the...
Replies
7
Views
329
Just purchased Studio5000 and have it installed, will be connecting to 3 brand new Powerflex 7000 VFDs. In setting up the module, how can I tell...
Replies
7
Views
767
I have a contractor at my water plant installing 3 brand new Powerflex 7000 VFD's for my High Service pumps. I would like to control these via...