Powerflex 40p doesn't use commanded speed

AdamG8GXP

Member
Join Date
Jun 2011
Location
Chicago, IL
Posts
35
I have a Powerflex 40p VFD setup to be controlled by comm port ( parameters 36, 38) with 22-comm-e card. It works fine when it is turned on but by 3rd start command it overwrites Commanded Freq with maximum value. It still runs and stops when PLC tells it but only at full speed.
Also parameter 12, control source when it starts is 52, and then changes to 12.
Parameter 14, Dig in status stays at all 0s.
I also noticed that in RSLOgix5000 V 20.01 when I open VFDs properties it says "Module Properties:Local:0" in title bar, and other VFDs in same project (all 40p) show "Module Properties:Local" without zero at the end.
It is run by 1769-L36ERM CPU. CPU and VFDs are connected to network switch.
I have yet to try a different Ethernet cable.

Other drives on this machine were doing it also but after downloading parameters to them they stopped doing that. This didn't help this VFD.

I can provide more info if needed.

What else can I check or what am I doing wrong?
 
Last edited:

Similar Topics

Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
252
I'm in the process of replacing an existing powerflex 40p. The old one died with no software backup but we did have a printout of the parameters...
Replies
3
Views
1,221
How can I find the IP of a used Powerflex 40p? I have used them in the past I have a hand held programmer for the 22 Comm E that I used before...
Replies
4
Views
1,781
Is there a way in rsnetworx or connected components to compare 2 powerflex parameter sets? TIA P.S this is also my first post here so hello...
Replies
5
Views
2,246
I have P036 configured as 2 wire SRC Control with an exteranl supply. I choose the direction with a 3 point rotary switch. The problem is when it...
Replies
1
Views
1,166
Back
Top Bottom