Where do signals fq-100, fq-500 come from?


See Post #69:

so here they are

fq-100 is the flow out of p1
fq-500 is the flow out of p2
lt-100 is t1 level
lt-300 is t2 level
t-1000 is the decant tank ...


Anyway, success.

PV Max values are linear Kp (Assuming PV Min values are 0), so magnitudes can be dropped to bring Kp into whatever range (0-100) is necessary.

To get there, e.g. to 13.5 to 4095, when doing it in one step causes a process upset, it may be necessary to do it in steps e.g. 4095 => 3000 and increase Kp, 3000 => 2250 and increase Kp, etc. Or just put the controller in Manual, make the change, then put it back into Auto.
 
I have read Post #69. Is this data from flow sensors? Such noisy?


Yes, I have been assuming those are flow sensors. However, the PID output CV is being linearly scaled to be the VFD speed reference, so the flows are interesting but do not matter much.

Yes, they are pretty noisy. I don't know if that noise is from the noisy level through the CV, but it does not seem to be an issue.
 

Similar Topics

Hello, I am attempting to tune a PID loop on a process. The process involves a valve with electronic actuator that has quite a high deadband...
Replies
10
Views
2,193
Hi everyone, yet another PID problem. I'm hoping I understand enough of the process I'm controlling that my request for help is reasonable. If a...
Replies
113
Views
28,148
A few months ago, I started to look into PID controllers and the tuning of first order processes. This has, partly thanks to you, resulted in a...
Replies
162
Views
62,467
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
Replies
16
Views
4,117
Hello, there is anyone who have already used hpmont plc? now i am programming for that plc and have " pid autotuning is not working" issue. I have...
Replies
0
Views
978
Back
Top Bottom