Hello
Is possible to communicate an PLC Omron CJ2M CPU33 with HMI thorough Modbus TCP, if is possible, how? whats is de modbus map register
Thanks
 
Yes but you will need a CJ1W-ETN21 Ethernet card and a function block from Omron (free). The function block uses sockets and the onboard EIP Ethernet port does not have sockets. You make your own register map in the PLC.
 
Hello
Is possible to communicate an PLC Omron CJ2M CPU33 with HMI thorough Modbus TCP, if is possible, how? whats is de modbus map register
Thanks

If your HMI have Ethernet/IP or OMRON protocol you can connect them directly.
But if you really need to use Modbus TCP you can use function block on OMRON website below with CJ1W-ETN-21 to be Modbus TCP server.

https://www.myomron.com/index.php?action=kb&article=1245
 

Similar Topics

Is it possible to use the same ethernet card (ETN21) for HMI connection and also for Modbus TCP/IP server, connection are via a standard switch...
Replies
11
Views
9,813
I would like to do some very simple MODBUS RTU communication using the built in port in CJ2M-CPU1[] I have been reading in the forums and manuals...
Replies
3
Views
5,945
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
Replies
5
Views
188
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
76
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
3
Views
125
Back
Top Bottom