TimD
Lifetime Supporting Member
f
then the next most likely cause for the "8 volt power supply drop" effect that you reported would be that the power supply is "floating" – and the meter connection is merely providing a path to "ground" ... in other words, it doesn't sound like the power supply is tied to a firm "ground" potential ... in most cases that's a recipe for "noise" and "fluctuation" from the input signals ...
Hi Ron,
I did switch PSUs (same ratings) and the same behavior is present. The grounds on the supplies are tied together. I also noticed that the panel shop did not ground the PLCs or supplies to the panel itself, as mentioned in Allen Bradley's Grounding and Control Wiring standards manual. Maybe doing this will help as well. I will probably tie an additional ground today to earth somehow. (8' rod...) May not have the time for that though.
First thing is for me to use the on-board instrument supply from the controller and hook up one sensor. I am going to hook it up in it's native NPN configuration without pull-up resistor. Apparantly, I have this configuration already, but never got the meters to 'talk' without using a resistor. I have 24v- to common, and 24v+ through sensing element and onto plc input, this is exactly as described in both PLC hardware manual, and Omega's Flow Meter manual. I never could get the plc to read anything until I introduced a resistor, which kept the input high. I am still perplexed as to why I need the resistor, when both manuals do not call for one, and the inputs can be configured NPN or PNP on the controller...