Hi all,

We are facing synching issues with redundancy module, where the Primary is ending up with disqualified secondary. Normally this would happen due to a coding issue where there is watchdog timer failure, and that results in some Minor and major faults too. this time though, there are no Minor or Major Faults as well. I dont understand why this is happening, and what can be the possible solution. Pls refer to the attached pic for reference.

ss1 plc issue.png
 
Every release bundle of firmware for ControlLogix Redundancy comes with a Redundancy Module manager utility, which will give you more information about the reason and timing for the disqualification of the Secondary.

That utility's installer is bundled with the firmware kit.
 

Similar Topics

Dear Team, I need experts advice on how to resolve the problem below : We have two 1756-L55 RSLogix5000 Controllers installed in a redundancy...
Replies
5
Views
1,834
Hi Experts, I need to test if a ControlLogix redundancy system will switchover when the Primary chassis has a major fault occurred. I followed...
Replies
2
Views
1,860
Dear All We have SIEMENS PLC S7-412-3H redundant system having remote I/O modules connected with Profibus. During commissioning when we Power up...
Replies
0
Views
2,312
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
103
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
214
Back
Top Bottom