Updating OS on Siemens OP77B

russg

Member
Join Date
Aug 2012
Location
UK
Posts
275
Hi, I'm trying to modify the OB77B screen, but it says I need to update the operating system because I'm using a newer version of WinCC. I'm using WinCC 2008 SP3. When I try to update, it says transfer aborted. I'm struggling to understand why. I'm connected to the S7-300 fine, and there must be some communication if it knows I need to update the OS? I've tried different baud rates and connection types. Do you sometimes need to go to a transfer mode on some of the OP units?

Thanks

Russ
 
Do you sometimes need to go to a transfer mode on some of the OP units?
Depends on how the panel is setup. I dont know OP77B, but on other panels you can setup the panel to allow remote control of the transfer mode.

Just set it to transfer mode, start the OS Update and see how it goes.
 
Hi, thanks for your reply. I'm just trying now to update the OS but i'm getting the message
"the target device is not supported by the current command"
 
yes, i think so. I choose transfer on the panel then it says transferring..... connecting to....
 

Similar Topics

First, I have to state that I am NOT an engineer. I'm just a garden variety industrial electrician who has been in the game for a long time...
Replies
4
Views
2,204
Hi there, Following procedure for updating software on 6RA7013, stuck at step 5 (for those who have the manual) where you open a dos window and...
Replies
5
Views
4,293
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
Replies
1
Views
72
Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
Replies
3
Views
128
Is there anything I Should take into account while updating the firmware on a safety processor? I have a 1756-L61S running version 17 and need...
Replies
0
Views
103
Back
Top Bottom