Bob O Member B Join Date May 2003 Location Posts 1,875 Aug 29, 2019 #16 Is the other device a SLC PLC? Try the laptops built in serial port. I think that would be 0 but it's been so long since I've had a real serial port.
Is the other device a SLC PLC? Try the laptops built in serial port. I think that would be 0 but it's been so long since I've had a real serial port.
JesperMP Lifetime Supporting Member + Moderator Join Date Feb 2003 Location ᚴᚬᛒᛅᚾᚼᚬᚠᚾ Posts 16,361 Aug 29, 2019 #17 You have baudrate 9600. Default is 19200 baud. I think that for some old CPUs the default was 1200 baud. So try with 19200 and 1200.
You have baudrate 9600. Default is 19200 baud. I think that for some old CPUs the default was 1200 baud. So try with 19200 and 1200.
Bob O Member B Join Date May 2003 Location Posts 1,875 Aug 29, 2019 #18 Sorry for throwing a lot of questions at you but what are the LEDs doing on the controller?
Lucatiel Member OP L Join Date Aug 2019 Location Swiebodzin Posts 9 Aug 29, 2019 #19 OK, Topic can be closed. I had a problem with power supply and SLC didn't run properly (something new for me, but instead of 24VDC I got 3-18VDC. I don't know why was that. Thanks for help anyway!
OK, Topic can be closed. I had a problem with power supply and SLC didn't run properly (something new for me, but instead of 24VDC I got 3-18VDC. I don't know why was that. Thanks for help anyway!