Hi all, it's my first thread in this forum.
I have problem with eem instruction. I try to communicate my slc 5/05 with alarm system and all time I had error:
"Connection not completed before user-specifed timeout"
In alarm integration port is 12850 and I dont know where I must put this port. I wrote port in MultiHop after IP adress but its doesn't work.

P.S. Sorry for my english
 
First things first.

Do a PING from your computer to see if you can get to the address of the device you want to communicate with.

Post screenshots of your configuration windows as well.

You also need to check the default gateway configuration for the SLC 5/05 and for the device you are communicating with. You could be having issues with the devices being on different subnets or vlans and we need to narrow the cause down a little bit.
 
Welcome to the Forum !

Are you certain that your alarm system supports the same application-level protocols as the SLC-5/05 ?

Rockwell Automation's Control and Information Protocol (CIP) is often referred to by a trade name, "EtherNet/IP", for "Industrial Protocol".

This is not the same as general-purpose Internet Protocol.

Rockwell's EtherNet/IP uses TCP Port 44818 for explicit messaging, including the EEM instruction in the SLC-5/05 controller.

Sending a generic Ethernet message to TCP Port 12850 will very likely require a network gateway or translator.
 
Make sure you check the firmware level in the 5/05.
Many early versions had problems communicating on different octets no matter what the mask was set at.

Depending on the hardware the latest is either C-11 or C-13.

If you have a support contract you can download the latest from AB.com.

Fore warning...it can be a challenge to get the right setup for
Flashing 5/05s.
 
I checked configuration again and you have right, in slc gateway was 0.0.0.0. When I change gateway I have no error in eem instruction. Thx U wery much 🍻
Now I must think what I do wrong because alarm dont response for frame
 
What kind of alarm system is it ?

Does it support the EtherNet/IP application protocol ?

What service/class/instance/attribute values are you using in the EEM instruction ?

Has the vendor of the alarm system given you examples of using it with the SLC-5/05 controller ?
 
What kind of alarm system is it ?

Does it support the EtherNet/IP application protocol ?

What service/class/instance/attribute values are you using in the EEM instruction ?

Has the vendor of the alarm system given you examples of using it with the SLC-5/05 controller ?

1: Satel integra
2: yes its support, I have description of Protocol
3: Service: custom, class 1, instance 1, attribute 1
4: No I haven't example for slc500, I have example for wago but not in ladder, its structured text

FUNCTION_BLOCK SatelEthernet
VAR_INPUT
xOpen_Client: BOOL; (* uaktywnij polaczenie do modulu ETHM-1 *)
IP: STRING; (* adres IP modulu ETHM-1 *)
Port: WORD; (* port integracji modulu ETHM-1 *)
END_VAR
VAR_OUTPUT
czujki: ARRAY [1..64] OF BOOL; (* tablica zawierajaca stany czujek od 1 do 64, TRUE - czujka aktywna *)
strefy: ARRAY [1..32] OF BOOL; (* tablica zawierajaca stany stref od 1 do 32, TRUE - strefa uzbrojona *)
wyjscia: ARRAY [1..64] OF BOOL; (* tablica zawierajaca stany wyjsc od 1 do 64, TRUE - wyjscie aktywne *)
xCLIENT_OPEN: BOOL; (* polaczenie do modulu ETHM-1 aktywne *)
wSOCKET: WORD; (* numer wtyczki *)
END_VAR
VAR
Protocol : SEL_PROTOCOL := IPPROTO_TCP; (* wybrany protokol transmisji - TCP *)
ProtocolType : SEL_TYPE := SOCK_STREAM; (* wybrany typ trasmisji - stream *)
MyEthernetOpen : ETHERNET_CLIENT_OPEN;
MyEthernetClose : ETHERNET_CLIENT_CLOSE;
MyEthernetWrite : ETHERNET_WRITE;
MyEthernetRead : ETHERNET_READ;
Read00 : BOOL := TRUE; (* zadanie wyslania polecenia 00 - odczyt stanu czujek*)
Read0A : BOOL := TRUE; (*zadanie wyslania polecenia 0A - odczyt stanu uzbrojenia alarmu *)
Read17 : BOOL := TRUE; (* zadanie wyslania polecenia 00 - odczyt stanu wyjsc*)
fi: INT; (* pierwszy indeks ramki *)
fin: INT; (* drugi indeks ramki *)
buf_len: WORD; (* dlugosc danych w buforze *)
znacznik: BYTE := 1; (* znacznik uzywany do operacji bitowych *)
pt: POINTER TO ARRAY [1..1500] OF BYTE; (* wskaznik do tablicy - uzywany przy przkazywaniu tablicy do funkcji *)
frame_rcv: ARRAY [1..1500] OF BYTE; (* tablica danych odebranych *)
frame_snd: ARRAY [1..1500] OF BYTE; (* tablica danych wysylanych *)
Status: WORD := 0; (* status transmisji: 0 - inicjalizacja, 1 - sprawdzenie stosu TCP/IP 4 - inicjalizacja otwarcia polaczenia, 5 - oczekiwanie na otwarcie polaczenia, 10 -wyslanie danych do serwera, 20 - oczekiwanie na odbior danych, 30 - interpretacja otrzymanych danych, 40 - zamykanie polaczenia *)
GetConfig: ETHERNET_GET_NETWORK_CONFIG;
utERROR: ETH_ERROR;
closeState: INT; (* status zamykania polaczenia *)
Timeout: TOF_1 := (PT:=T#2s, IN:=TRUE, RST:= FALSE); (* maksymalny czas oczekiwania na odpowiedz ze sterownika *)
END_VAR

IF xOpen_Client THEN

CASE Status OF
0:(*Initialize functionblocks*)
GetConfig(EN:=FALSE );
GetConfig(EN:=TRUE );
status:=1;
utERROR:=0;
wSocket:=0;
closeState:=0;
xCLIENT_OPEN:=FALSE;


1:(*check ethernet stack*)
GetConfig(EN:=TRUE );
IF GetConfig.ENO THEN
IF GetConfig.IP_ADR<>0 THEN
status:=4;(*stack initialized*)
ELSE
status:=0;(*try again*)
END_IF
END_IF


4:(*open connection*)
MyEthernetRead( EN:= 0, SOCKET:=0 , DATA:=frame_rcv );
MyEthernetClose(EN:= 0);
MyEthernetOpen(EN:=0);

MyEthernetOpen(EN:=1 , TYP:=ProtocolType , PROTO:=Protocol , IP_ADR:= IP_ADDRESS(IP), PORT:=Port );
status:=5;

5:(*wait for server response according to client request to open the connection*)

MyEthernetOpen(EN:=1, TYP:=ProtocolType, PROTO:=Protocol, IP_ADR:= IP_ADDRESS(IP), PORT:=Port );
IF MyEthernetOpen.ENO = 1 THEN
IF MyEthernetOpen.ERROR = 0 THEN
Status := 10; (*socket available*)
xCLIENT_OPEN:=TRUE;
wSOCKET :=MyEthernetOpen.socket;
MyEthernetWrite( EN:= 0 , DATA:=frame_snd );
ELSE
Status := 0; (*no socket available, try it again *)
END_IF;
utERROR:=MyEthernetOpen.ERROR;
END_IF


10:(* Write data to server*)

frame_snd[1]:=16#FE;
frame_snd[2]:=16#FE;
IF Read00 THEN
frame_snd[3]:=16#00; (* zapytanie o stan czujek *)
ELSIF Read0A THEN
frame_snd[3]:=16#0A; (* zapytanie o stan uzbrojenia alarmu *)
ELSIF Read17 THEN
frame_snd[3]:=16#17; (* zapytanie o stan wyjsc *)
ELSE
frame_snd[3]:=16#7F; (* zapytanie o zmiane stanu *)
END_IF
pt:=ADR(frame_snd);
frame_snd[4]:=WORD_TO_BYTE(SHR(SatelCRC(pt,3,3),8)); (* obliczenie CRC.H *)
frame_snd[5]:=WORD_TO_BYTE(SatelCRC(pt,3,3)); (* obliczenie CRC.L *)
frame_snd[6]:=16#FE;
frame_snd[7]:=16#0D;
MyEthernetWrite(EN:= 1,SOCKET:= MyEthernetOpen.SOCKET, LEN_IN:=7,DATA:=frame_snd); (* wyslanie ramki *)
IF MyEthernetWrite.eno THEN
IF(MyEthernetWrite.ERROR <>0) THEN
Status:=40; (* Error writing to the socket, close it *)
ELSE
Status:=20; (* Write complete, read data *)
END_IF;
utERROR:=MyEthernetWrite.ERROR;
END_IF
Timeout (IN := FALSE);


20: (* Read data*)

MyEthernetRead( EN:= 1, SOCKET:=MyEthernetOpen.SOCKET , DATA:=frame_rcv );
MyEthernetRead( EN:= 0, SOCKET:=0 , DATA:=frame_rcv );

Timeout (IN := FALSE);
utERROR:=MyEthernetREAD.ERROR;
IF(MyEthernetRead.ERROR<>0) THEN (* Error reading the socket, close it *)
Status:=40;
ELSIF (MyEthernetRead.LEN_OUT <> 0) THEN (* Process the data received via the ethernet port *)
Timeout(IN := TRUE);
Status:=30;
ELSIF NOT Timeout.Q THEN
Timeout(IN := TRUE);
Status:=10; (* uplynal czas oczeiwania na odpowiedz, zerowanie licznika i ponowne wyslanie zapytania *)
END_IF

30: (* Process received data *)

buf_len:=MyEthernetRead.LEN_OUT;
FOR fi:=3 TO buf_len-4 DO (* sprawdzenie, czy bajt odebranej ramki nie zawiera kombinacji FE F0; w takim przypadku wyrzuc F0 i skroc odebrane dane *)
IF frame_rcv[fi]=16#FE THEN
IF frame_rcv [fi+1]=16#F0 THEN
FOR fin:=fi+1 TO buf_len-2 DO
frame_rcv[fin]:= frame_rcv[fin+1];
END_FOR
buf_len:=buf_len-1;
END_IF;
END_IF;
END_FOR;
pt:=ADR(frame_rcv); (* przekazanie adresu znacznika danych odebranych - potrzebne do przekazania danych do obliczenia CRC *)
IF frame_rcv[buf_len-3]=WORD_TO_BYTE(SHR(SatelCRC(pt,3,buf_len-4),8)) AND frame_rcv[buf_len-2]=WORD_TO_BYTE(SatelCRC(pt,3,buf_len-4)) THEN (* sprawdzenie poprawnosci CRC otrzymanych danych *)
IF frame_rcv[3]=16#7F THEN (* jesli otrzymano ramke zapytania o zmiane stanu *)
(*Com7FReceived:=Com7FReceived+1;*)
IF (frame_rcv[4] AND znacznik) >0 THEN (* sprawdzenie czy bit 0 pierwszego bajtu danych jest 1, czyli stan czujek ulegl zmianie *)
Read00:=TRUE; (* jesli tak, nastepnym razem zapytaj o stan czujek *)
END_IF;
IF (frame_rcv[5] AND ROL(znacznik,2)) >0 THEN (* sprawdzenie czy bit 2 drugiego bajtu danych jest 1, czyli stan stref ulegl zmianie *)
Read0A:=TRUE; (* jesli tak, nastepnym razem zapytaj o stan stref*)
END_IF;
IF (frame_rcv[6] AND ROL(znacznik,7)) >0 THEN (* sprawdzenie czy bit 7 trzeciego bajtu danych jest 1, czyli stan wyjsc ulegl zmianie *)
Read17:=TRUE; (* jesli tak, nastepnym razem zapytaj o stan wyjsc*)
END_IF;
ELSIF frame_rcv[3] = 16#00 THEN (* jesli otrzymano ramke stanu czujek *)
(*Com00Received:=Com00Received+1;*)
znacznik:=1;
FOR fi:=4 TO buf_len-5 DO (* dla kazdego bajtu danych *)
FOR fin:=0 TO 7 DO (* dla kazdego bitu *)
IF (SHL(znacznik,fin) AND frame_rcv[fi]) >0 THEN (* sprawdz czy bit jest 1 *)
czujki[(fi-4)*8+fin+1]:=TRUE; (* jesli tak stan czujki = TRUE - aktywna *)
ELSE
czujki[(fi-4)*8+fin+1]:=FALSE; (* jesli nie = FALSE - nieaktywna *)
END_IF;
END_FOR;
END_FOR;
(*AktCzujek := TRUE;*)
Read00 := FALSE;; (* nastepnym razem nie pytaj o czujki *)
ELSIF frame_rcv[3] = 16#0A THEN
FOR fi:=4 TO buf_len-5 DO (* dla kazdego bajtu danych *)
FOR fin:=0 TO 7 DO (* dla kazdego bitu *)
IF (SHL(znacznik,fin) AND frame_rcv[fi]) >0 THEN (* sprawdz czy bit jest 1 *)
strefy[(fi-4)*8+fin+1]:=TRUE; (* jesli tak stan strefy = TRUE - uzbrojona *)
ELSE
strefy[(fi-4)*8+fin+1]:=FALSE; (* jesli nie = FALSE - rozbrojona *)
END_IF;
END_FOR;
END_FOR;
Read0A := FALSE; (* nastepnym razem nie pyatj o strefy *)
ELSIF frame_rcv[3] =16#17 THEN
FOR fi:=4 TO buf_len-5 DO (* dla kazdego bajtu danych *)
FOR fin:=0 TO 7 DO (* dla kazdego bitu *)
IF (SHL(znacznik,fin) AND frame_rcv[fi]) >0 THEN (* sprawdz czy bit jest 1 *)
wyjscia[(fi-4)*8+fin+1]:=TRUE; (* jesli tak stan wyjscia = TRUE - aktywne *)
ELSE
wyjscia[(fi-4)*8+fin+1]:=FALSE; (* jesli nie = FALSE - nieaktywne *)
END_IF;
END_FOR;
END_FOR;
Read17 := FALSE; (* nastepnym razem nie pyatj o wyjscia *)
END_IF;
END_IF;
Status:=10; (* przejdz do wysylania danych *)
MyEthernetWrite( EN:= 0 , DATA:=frame_snd ); (* przygotuj nadajnik do nadawania *)

40: (* Close the client *)

MyEthernetClose(EN:= 1, SOCKET:= MyEthernetOpen.SOCKET);
IF MyEthernetClose.eno THEN
MyEthernetClose(EN:= 0);
xCLIENT_OPEN:=FALSE;
Status := 0; (* Try to open the server again *)
END_IF

END_CASE;
ELSE
CASE CloseState OF
0:
MyEthernetClose(EN:= 0);
MyEthernetClose(EN:= 1, SOCKET:= MyEthernetOpen.SOCKET);
CloseState:=1;
1:
MyEthernetClose(EN:= 1, SOCKET:= MyEthernetOpen.SOCKET);
IF MyEthernetClose.eno THEN
MyEthernetClose(EN:= 0);
CloseState:=2;
END_IF
2:
Status := 0;
utERROR:=0;
xCLIENT_OPEN:=FALSE;
END_CASE
END_IF
 
That Wago structured text shows a TCP socket stream, not an EtherNet/IP application protocol connection.

I've read the protocol manual for the ETHM1 Plus interface and there is no evidence that it supports EtherNet/IP.

You might have better success implementing this with a Serial -> Ethernet -> Serial connection so you can use the ASCII port of the SLC-5/05 controller.

Or, you could try an EtherNet/IP to Generic Ethernet bridge module. The RTA Automation devices should do what you need.

http://www.rtaautomation.com/product/490490nba/
 
That Anybus device works well with the ControlLogix and CompactLogix family controllers, and supports serial protocols (not Ethernet) on the other side. I expect that your alarm system also has a serial port.

But I do not know of any way to use the Anybus gateway with an SLC-5/05 controller. The Anybus needs a cyclic I/O connection, and the SLC-5/05 cannot create one over EtherNet/IP.

How far is the alarm system from the SLC-5/05 controller ? Is the Channel 0 serial port of the SLC-5/05 in use ?
 
Ahh I think that I can use Ch 0 to serial in AnyBus. I see I was wrong.
In this situation I dont try use ethernet to communication and just buy rs module to integration, this is easier and cheaper way.
Thx a lot Ken.
 

Similar Topics

I have some equipment with Allen Bradley SLC 504 PLC's, that have a Prosoft MVI46 ethernet module installed. I would like to configure it to talk...
Replies
1
Views
3,154
I am trying to set up the communication between a SLC 5/05 and a Schneider ATV71 drive with an Ethernet I/P communication module. I believe this...
Replies
8
Views
6,094
Hello all dear PLC Lovers, I am using SLC5/05 (1747-L552). I want to establish the communication between the SLC and my notebook via Ethernet...
Replies
7
Views
6,032
Hi, I have a problem with a cpu slc 5/05 (1747-L552), 32k Mem 0S501 series C, I am using the MSG instruction to ethernet communication, it works...
Replies
13
Views
9,291
Hello fellow techies, I am using a BSN modules to switch RIO on a redundant SLC500 project (I didn't spec the hardware). The design has one pair...
Replies
17
Views
16,075
Back
Top Bottom