I have some equipment with Allen Bradley SLC 504 PLC's, that have a Prosoft MVI46 ethernet module installed. I would like to configure it to talk to a Control Logix5555 processor over ethernet. I understand how to configure the SLC 504 and Prosoft card, but I do not know how to configure the Logix5555 processor. Do I configure it as IO, or do I use messaging? I'm so used to these old SLC's that I'm starting from scratch here with the Logix5555.

Thanks!
 
Welcome to the Forum!
Unfortunately you will not be able to exchange data between the CLX and SLC CPUs via implicit communications (I/O Class); you will have to use explicit messaging (MSG) over Ethernet.
Also, the SLC Data Table addresses to be accessed by the CLX controller will need to be "translated" into Logix Tags using the RSL5K "Map PLC/SLC Data..." tool and only then referenced by the RSL5K application MSGing logic.
 

Similar Topics

I have a system that is using TCP sockets. There are 5 connections between the Ethernet card and the end devices (smart conveying system)...
Replies
0
Views
711
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
Replies
7
Views
2,207
Hi I’m having issues figuring out how to connect a Schneider ATV930 to Control Logix PLC. Can’t figure out the Connection Parameters, I used the...
Replies
2
Views
1,202
Hi I’m having issues figuring out how to connect a Schneider ATV930 to Control Logix PLC. Can’t figure out the Connection Parameters, I used the...
Replies
0
Views
1,011
Hello. I am still fairly new to this. I am playing around with an Indradrive HCS01 controller. I have it talking to my L71 (V33.11) just fine...
Replies
2
Views
2,356
Back
Top Bottom