Profibus: ET200M hooked up with Experion PKS

Wooter

Member
Join Date
Feb 2006
Location
Tessenderlo
Posts
2
Hello,

I have coupled a Siemens ET200M remote IO module (6ES7 153-2BA00-0XB0) with an Honeywell Experion PKS system (Release 211) through a profibus SST-PFB-CLX-RLL card. I uploaded the correct GSD file in the SST card. All DI, DO, AI signals work fine.
The only problem remaining is that I don't get 4-20mA out of the AO card (332-5HD01-0AB0). I only get 0-10 V out of it, even if I configure it for 1-5V, 4-20mA, 0-10V (both in the SST card and in the Honeywell DCS).

[font=Arial,Bold]any ideas about how to fix this problem.[/font]
[font=Arial,Bold][/font]
[font=Arial,Bold]best regards
[/font]
 
6ES7 332-5HD01-0AB0
Analog output module AO4/12 bits, reconfigurable online
Is what I get on the card - do you have a 300 series processor with a profibus port available for a test ?
How do you download the config to the bus module as it stands ?
 

Similar Topics

I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
558
Hi guys, I have a problem in profibus communication between IPC with FC3101 from BECKHOFF(Master)and two et200m(slave). The problem is when I...
Replies
0
Views
1,300
Hello, I am trying to communicate to an RS485 device via a CP-340 RS485 card attached to an IM-153-1 communications processor in an ET200M remote...
Replies
5
Views
5,171
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
197
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
92
Back
Top Bottom