Yes sir.
Although It'd be more fun if i didn't have other head scratchers to contend with.
There are two stations doing exact same thing, Drive A220 and A225. A 225 has more overshooting but both problematic.
Alarm gives generic message saying Mechanical anomaly or overheat. No faults on the Drive itself. Alarm (113) is coming from S01200 tag A225_Errore (bool) which is in S10211 MOV_Guide(A225_moveguide............,A225_Errore,.........) Where is that coming from?
To confuse matters, There's also a tag A225_Error (not Errore)
I have swapped A220,A225 drives and overshoot problems did not follow Drive.
IP for A225 is 192.168.1.36
Mechanically it's been completely looked over by myself and Machine guys.
Thanks for digging into the mystery with me.
Although It'd be more fun if i didn't have other head scratchers to contend with.
There are two stations doing exact same thing, Drive A220 and A225. A 225 has more overshooting but both problematic.
Alarm gives generic message saying Mechanical anomaly or overheat. No faults on the Drive itself. Alarm (113) is coming from S01200 tag A225_Errore (bool) which is in S10211 MOV_Guide(A225_moveguide............,A225_Errore,.........) Where is that coming from?
To confuse matters, There's also a tag A225_Error (not Errore)
I have swapped A220,A225 drives and overshoot problems did not follow Drive.
IP for A225 is 192.168.1.36
Mechanically it's been completely looked over by myself and Machine guys.
Thanks for digging into the mystery with me.