I have a problem! I have a PLC project with a 1756_L73 CPU from allen Bradley, and I need to read variables from an energy analyzer SIEMENS SENTRON PAC3100 (7km3133-0ba00-3aa0) via MODBUS RTU, can anyone send me an example? it seems that my CPU doesn't have native modbus RTU port.
Tanks in advance!!
 
Welcome to the Forum !

You are correct; the 1756-L73 does not have a native Modbus RTU port. In fact, it has no serial port at all.

If the Siemens meter has only a Modbus RTU serial port, then you need to select a network to Modbus converter first.

There are quite a few EtherNet/IP to Modbus RTU bridge and converter devices. I strongly prefer the HMS Fieldbus "Anybus Communicator".

I cannot tell for certain if the Siemens meter has RS-232 serial port wiring, or if it is RS-485, or something else. That is one of the things you should also try to figure out.
 
Last edited:
I looked at a quick spec sheet for the Sentron and it appears to be RS-485.

There are several ways to get the data you need. As Ken as stated you will need to add something to the system to talk Modbus to the Analyzer. I have used the Red Lion DataStation Plus to do the Protocol conversion between a AB Plc and a Modbus device ($1,500 US). If you project needs a HMI in it you can also use a Red Lion HMI as it has the same protocol conversion function as the DataStation Plus ($800 on up depending on the size). Both of these solutions are very easy to configure and I have had great luck with the service life of the Red Lion products I have used in the past.

If you want a solution that plugs into the Chassis of your PLC then Prosoft makes several different Modbus Communication cards that work very well. They can be expensive (around $3,000 US) and are more complicated to use than other solutions. If you have a Point I/O System attached to your PLC, Prosoft has a card that will work with the Point I/O and is much more reasonably priced ($1,500 US). It only has Serial Communications but should work for your application.

Any more questions come on back,
 
You may use an AB Micro850PLC with 2080-SERIALISOL Plug-ins as a gateway.

Micro850PLC with 2080-SERIALISOL support Modbus RTU (RS232 and RS485)

MSG instruction can be used to communicate between Micro850PLC and 1756-L73.

And more important, Micro850PLC is quit cheap actually.
 
We have an Ethernet IP to Modbus Gateway.
http://www.icpdas-usa.com/gw_7472.html
3811_1448992261.jpg
 

Similar Topics

Hi all ! I can't figure out how to setup the modbus RTU comm. to connect a Koyo DL250-1 CPU with a Panelview Plus 600 from Allen-Bradley. I use...
Replies
8
Views
3,975
I'm trying to communicate to a Modbus RTU slave device using an M340 as the Modbus master using READ_VAR and WRITE_VAR. I'm connecting directly...
Replies
1
Views
7,997
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
52
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
233
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
272
Back
Top Bottom