I've been trying to get Modbus TCP to communicate (read only) with the Modbus TCP AOI that Rockwell provides, but I'm having issues and was wondering if anyone might help.

What I'm seeing is that when I try to poll holding registers (34 total), it only reads about ten of them. Sometimes I'll get an STS_Overload alarm, sometimes not but the status of the transaction always says "exception".

I've read through the documentation and have been playing with the Periodic Task's execution period, as well as the AOI's Poll Interval but nothing seems to fix it. Thanks for any help!
 
Can you post your ACD upload in faulted state, and wireshark?
Modbus Slave device manual would help too.

Overlap means that your peer device did not respond before next scheduled read attempt.
Since you have an exception, then you can read exception code.
I would say that you are trying to read something that device does not support.
 
If you can't post your full ACD, then do upload, export one AOI rung only and post that rung. Rung import will contain all configuration and exception values
 

Similar Topics

Hello, I'm in need of a solution to send data from RSLogix5000 PLC to a couple of heating controllers that have an RS232 Modbus interface...
Replies
4
Views
1,963
Hey gang - I can't seem to locate any decent sample code for accomplishing what i need to do. I have a CompactLogix L23E, connected via...
Replies
18
Views
14,651
Hi Guys! Since I have been a fix with protocols not being the same before, I'll ask if any of you have ever tried this combination: I have a...
Replies
3
Views
6,475
Hi! So my problem is a little funky, I had Studio 5000 v 24 and 30 installed, but forgot to install RSLogix (which I cannot go without). Is there...
Replies
2
Views
123
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
Replies
15
Views
428
Back
Top Bottom