Hi,

Again, a topic about Kinetix 5100 servo drives. The controller is L33ER. The servo drive are 2198-E1020-ERS with a TLP-115-200-DJMC2A.

There are 2 servo motors with a leadscrew for mechanical transmission that move a heater up and down. The longer part of the motion is with absolute motion using the adapted MAM Add-On Instruction for Kinetix 5100. The other part of the motion is in torque mode using the adapted MAT Add-On Instruction for Kinetix 5100.

The torque reference that is set is 140% of the rated torque of the motor that is 6.37 N*m. therefore the torque reference is about 8.9 N*m.

And at a random moment the drives gets error E02C that is said to be Drive Overload.

The motor is rated to have a peak torque of about 300% of the rated torque therefore the peak torque should be about 20 N*m.

After a lot of troubleshooting and monitoring different variables, I found a counter for the E02C error that increases when you are above the OverloadWarningUserThreshold parameter that is set to be, by default, to its maximum value 120%.

If you go at nominal torque 100% torque reference the counter decrements. If the counter reaches 100 the error E02C occurs.

The question is how can the peak torque or fraction of the peak torque be achieved without getting this error?

Best Regards
Konstantin Kolev
 

Similar Topics

Hello, I'm in the process of converting a slicer from an Ultra3000 drive to a Kinetix 5100 using the KNX software version 4.00. The current...
Replies
0
Views
538
Hi, I have a project where one of the modules is a gantry type structure with 2 servo motor, one from each side of the gantry. The transmission...
Replies
8
Views
1,740
There is a new Micro 850E that allows you to do implicit messaging to a Kinetix 5100 servo and a Powerflex 525. I can't seem to find any...
Replies
6
Views
1,972
Im teaching mechatronics in a community college. We were advised to get into Servo drives and the 5100. We downloaded and ran KNX5100C and it...
Replies
10
Views
3,882
Hello all! I am trying to integrate a Kinetix 5100 servo drive into a shipping system. I am upgrading from a Ultra 3000 drive, and the purpose of...
Replies
4
Views
1,883
Back
Top Bottom