Hi Guys,

Is it okay to have Redundancy ControlLogix Processor IP address set to DHCP?
I had Static IP address on it but removed it via RSLinx, the only option it allowed for IP removal was enabling DHCP.

When I connect via Stratix 5700 Managed switch Port (assigned smart port role = Desktop for Automation), I can't go online with the CPU via EN2TR ; but if I connect cable directly on the EN2TR it works.

Any ideas guys?
 
You should use static addresses with ControlLogix Redundancy. There are strict requirements for these.
See Redundancy user manual pages 29-31
Here is important note:
We recommend that you use static IP addresses on EtherNet/IP communication modules in redundancy systems. You cannot use dynamic IP addresses with IP address swapping.
 

Similar Topics

Hi, Looking at installing a L8x redundancy system and have perused the manual. Yep version 1 (beta..) on L8x, probably not the best idea, as well...
Replies
2
Views
1,421
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
3
Views
53
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
137
Hi, I wanted to ask is there a way to have a visibility expression use the IP address of the HMI (Dynics, not PV) to show certain elements? The...
Replies
3
Views
211
Hello. I have a few machines that use Kinetix 300 (each machine has two drives). Both drives on one of the machine keep losing IP address. They...
Replies
2
Views
105
Back
Top Bottom