Interface Ignition SCADA ethernet network to an Allen Bradley SLC5/04 Serial RS232

ControlSystems

Lifetime Supporting Member
Join Date
Dec 2020
Location
Presscot AZ
Posts
17
Hey Everyone,
I need to Interface Ignition SCADA ethernet network to an Allen Bradley SLC5/04 Serial RS232 DF1. Has anyone out there found a low cost interface that might do this. We are trying to avoid making the customer replace the controller with a SLC5/05 ethernet controller because they have an installed AB HMI with DH+ connection...
 
I do believe the Maple System G-01 gateway could handle the job.

Looks like Maple G series does support DF1, never used them myself. The G03 is maybe obsolete now but if it's a one-off, it's listed at $99

Read/write tags back and forth to Ignition with Mqtt.

If the OP doesn't currently have MQTT server modules, then the cost is going to be more than the $1200 DF1 device. Keep it simple.

There is also the Moxa Mgate Eip3170, however that may mean you need Phil Turmel's EIP driver as the IA one is for direct to PLC only.

There may be other Moxa offerings, I have used them a lot just not with AB.
 

Similar Topics

My company is looking at using Ignition for our SCADA solution at a facility. What is your impression of Ignition as compared to WW System...
Replies
3
Views
2,667
Hey guys, I just wanted to see if any of the bright minds on here had any opinions on these relay interface modules. Particularly, I would love to...
Replies
1
Views
58
Hello world! The company I started working for has these valves that they ordered years ago as spares. now we have to add couple valves on...
Replies
6
Views
211
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
32
Views
914
Does anyone know why the connection interface is greyed out and says why I can only use Teleservice instead of the other options like PN/IE? I am...
Replies
5
Views
240
Back
Top Bottom