How can i connect Siemens PLC with modbus protocol?

ac-64-17-3e-fe-a7

That is a MAC address, more or less equivalent to a serial number of a particular individual PLC.

What was asked for was the model number, which usually starts with 6E e.g. something like this (source: ebay.com):
s-l500.png
 
Do you mean you have an ET200SP mounted S7-1510 or 1512, or is this just an ET200 remote IO with a separate PLC?

If it's the first one, yes this should allow you to communicate via Modbus TCP over the onboard ethernet port. You can do this with all S7-1200 and S7-1500 CPU's as far as I know.
 
Do you mean you have an ET200SP mounted S7-1510 or 1512, or is this just an ET200 remote IO with a separate PLC?

If it's the first one, yes this should allow you to communicate via Modbus TCP over the onboard ethernet port. You can do this with all S7-1200 and S7-1500 CPU's as far as I know.

This is the module, I can't uninstall it to see the module number in the other side

1.jpeg 2.jpg 3.jpg
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
357
Sorry for the basic question: At the moment, the PLC [S7-1200] is connected to a laptop (contains TIA Portal) via the ethernet port. When I add...
Replies
10
Views
1,543
Hi Complete newcomer to S7 so go easy on me... Siemens S7: What cable do I need to connect S7-1200 PLC to HMI? The touch screen is one of these...
Replies
14
Views
2,638
Hello guys, I have a siemens PLC and i want to add a new preocess without touch the Siemens code, so i am going to add Delta PLC, this PLC will...
Replies
11
Views
5,930
Hello, this is a brand new task for me. I recently bought a particulate sensor and it communicates with UART protocol or I2C protocol. It came...
Replies
12
Views
2,888
Back
Top Bottom