DASSIDirect through **** unit

lostcontrol

Lifetime Supporting Member
Join Date
May 2009
Location
NeverSayNever
Posts
1,071
Hi,
A customer has one of these units on a machine with a S7-300 PLC. The original intent was to use it for remote access via cell network, but we managed to change it to use customer internet, which has been very successful.

Now, we are wanting to use this as a gateway for the InTouch DASSIDirect IOServer.
But I am struggling to get the DAS Setup correct (I think). I dont really understand the Local/Remote TSAP, but know if I put the Remote at 0-2, the DAS gives me connection indication, but no values. I am not 100% that the values are as what is the PLC, as am not online to it yet.

What I want to ask, has anyone done something similar with this unit? Can you explain the TSAP config for me?
 
Hi, got this sorted.
the key was in the remote TSAP config, once I matched it to the actual setup rather than the default, the connection was established.
Then I had to do some siemens boot camp, trying to understand the config etc & pick registers that were being regularly updated...
 

Similar Topics

For those with experience with DASSIDirect, DASS7, and S7PLC-400's: Hi, I'm new in dealing with Siemens hardware. My coworker has already...
Replies
1
Views
5,067
I have a panel PC running Wonderware, and it has the DASSIDirect server running, I am trying to get it to talk to an S7-1500 PLC but without...
Replies
14
Views
4,996
Hello everyone, I am lookimg for some help to figure out where come from the problem or what i can do to improve the latency. PLC: S7 416-5h...
Replies
7
Views
3,021
Hello, please help me. I have big problem with communication between DASSIdirect 3 SP1 and S7-417H. I communicate over 5500 tags. There is VERY...
Replies
1
Views
3,846
Hi, I'm having some problems with values not updating. And mainly some that are only writing but not reading although they are set to read/write...
Replies
3
Views
4,159
Back
Top Bottom