Current Meter Recommendations

but the lowest sensing range is 0-50A which is a bit high, but I will see how it does. I will check these out for lower sensing ranges, so thank you for the recommendation.
If you need a lower range you can always run multiple turns of the power lead through a current transformer or transmitter.
1710083564365.png
 
I have had one bad AC current transducer in a batch of 12, so it can happen.

The transducer output is an active output so you'd think you'd get 4mA with no current on the sensed wire. But . . . .

1. The I/O module has the 4-20mA (-) connect to the L(-) terminal. If the 4-20mA is not an isolated output (which I doubtt given that terminals 2 & 3 are tied together on the transducer), you could have a ground loop problem between the transducer DC supply/transducer 4-20mA return and the I.O L(-).

Is there some reason you're not using the I/O modules L(+) for DC power to the transducer? The DCT100 needs 2VA or 85mA

2. The transducer is measuring DC current and the instructions are specific that the current flow must match the arrow on the device.

Is current flow (+) to (-) or (-) to (+)? Somehow, they forgot to specify and I'm old enough to remember debates about current flow, so I don't know what 'conventional' knowledge is for DC current flow. Is it worth changing the direction of the transducer on the sensed wire to check?
 
1. The I/O module has the 4-20mA (-) connect to the L(-) terminal. If the 4-20mA is not an isolated output (which I doubtt given that terminals 2 & 3 are tied together on the transducer), you could have a ground loop problem between the transducer DC supply/transducer 4-20mA return and the I.O L(-).

Is there some reason you're not using the I/O modules L(+) for DC power to the transducer? The DCT100 needs 2VA or 85mA
I previously testing the following wiring:
+Power -> L+
-Power -> L-
+OUT -> 4-20 analog input
-OUT -> empty

This displayed "UL" (Process value too low). I then swapped the analog input to -OUT and left +OUT empty and also get UL. I've tried reversing the transducer direction without success or any change to my outputs.

Perhaps @Tom Jenkins suggestion of lowering the sensing range could help?.. But shouldn't the baseline be 4 mA with no current regardless of the sensing range.
 
The DCT is a four-wire device, so I would eliminate the display unit from the circuit until the DCT configuration/function is verified. You can connect your meter to the 4(+) and 3(-) terminals directly. You should measure 4mA if there is no load. If you removed the range jumper to select the 0-50A range, 10A load should give you ~7.2mA output.
 
I agree with climtm. You need to confirm that the transducder/transmitter works on its own as a starting point.

Powering it with your DC power supply and connecting the output to nothing but a milliampmeter should tell you whether it is functional or not. You're right, even with no current on the sensing side, it should output 4mA.
 
I tested again with my multimeter with the following set up: I removed the display unit and +Power and -Power was connected to +V and -V of my 24V PSU. Red lead on MM on +Out and Black COM lead on MM on the -Out. I connected to power and confirmed it was receiving 24V, I got an output of 1.1mA... Safe to say there is an issue with the DCT?

It was a brand new unit, but I will try to get a new one to test... but now I wonder if I did damage to it any point in my testing? I at no point had an output from the DCT, so I don't think I did, but could me connecting directly to the PSU for power something that could cause damage to it over using the PLC module +24V supply?
 
I finally found a DCT200-42-24-S (split core, 100A) I had purchased last year, but haven't installed yet. With power connected and no load (I don't have anything close to 100A in my office), I see 4mA on the output. As danw said, it looks like you have a bad one.
 
I removed the display unit and +Power and -Power was connected to +V and -V of my 24V PSU. Red lead on MM on +Out and Black COM lead on MM on the -Out. I connected to power and confirmed it was receiving 24V
Got a new DCT and did the same testing I did above, this time I am getting 0.0-0.02mA. I have also tried using the +24V and GND from my PLC module for my + and -Power, with no output. I am using a HRP-150-24 PSU, is there some issue with the power supplies I am using or a different way I should try measuring this?
 
Is the fuse in the milliampmeter blown? Have you tested the meter on a known good 4-20mA DC circuit?

The transducer uses 2 VA, which at 24Vdc is 85mA. Your power supply is 150VA (6.5A) so it should handle a 2VA load. When everything is connected, the power supply still read 24V across its terminals, right?

The split core is closed? Jaws touch each other?

range jumper removed?

You've read the troubleshooting list on the installation page (bottom of page 2)?
https://cdn.automationdirect.com/static/manuals/acuampinserts/dct_installation.pdf
 
I recommend a Fluke 789 or 707 loop calibrator for anyone who deals with 4 to 20mA signals. I use mine all the time to validate my understanding of an instrument before landing the wires. These meters have a "Measure - Loop Power" mode that lets me test two wire devices completely isolated from control panel voltages, by supplying voltage to the device while measuring the returned current.

This one tool will help you keep the magic smoke inside the instruments and has probably paid for itself many times over.
 
Checked both mA and 10A fuses on the MM, they were good. The testing conditions are:
  • fixed core
  • jumper removed
  • no load/wire passing through center
  • 24V PS on pins 1 and 2
  • terminal screwed down on pins 3 and 4
Measuring across the output pins 3 and 4, I read 2.8 mV and 1.2 mA. I spoke with AD again and they recommended adding a resistor for load on the output terminals, and measuring for current in series. That's the last condition I can think of to test before assuming I have gotten a 2nd bad unit.
 

Similar Topics

I purchased a 4-20ma AC Current Transducer, it can be set to 0-100a, 0-150a, 0-200a. It is not True-RMS. This is connected to a panel meter and I...
Replies
1
Views
1,489
Dear experts, i have a CT 600/5A and analog Amps meter 0-600A @2.5Class, 1)now i want to measure the same current to changing analog meter to...
Replies
1
Views
2,410
My current project involves instrumentation for AC current. Input current range is 0-5 A (AC). Output of the device to be used has to be 4-20 mA...
Replies
2
Views
3,165
Today I was working on my project for school and we were using a power supply with 24V and we accidentally had the current at 0.9A. We heard a pop...
Replies
9
Views
553
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
667
Back