Compatible Modules for s7-300 6ES7312-1AE14-0AB0 PLC

oh and i've problem finding this 6ES7 334-0KE00-0AB0, AI 4/AO 2x12BIT, Sm334 . Is there any alternatives to it that will not change how it works and that i dont need to do anything else about it?

and it will have to work fine with that 1ae14 plc.
 
Last edited:
You could use the following, making sure that when you modify the hardware configuration, that the analog input and analog output addresses on each module are the same as on your 6ES7 334-0KE00-0AB0:

6ES7331-1KF02-0AB0 8 channel analog input module + 6ES7392-1AM00-0AB0 40-pin connector
OR
6ES7331-7KF02-0AB0 8 channel analog input module (more expensive) + 6ES7392-1AJ00-0AB0 20-pin connector

AND

6ES7332-5HB01-0AB0 2 channel analog output module + 6ES7392-1AJ00-0AB0 20-pin connector
OR
6ES7332-5HD01-0AB0 4 channel analog output module + 6ES7392-1AJ00-0AB0 20-pin connector
 
Thank you, i am sorry i couldnt reply earlier but you are a lifesaver, you've helped me so much. I would like to thank you for helping me this much.
 

Similar Topics

I'm not actually in front of the equipment yet, but this is the information that I have been given by a client: ------------ Data from HART...
Replies
2
Views
338
Hello, i can find the CPU when searching for it. But when I go Online i just get the icon for "Not compatible" everywhere. I get no additional...
Replies
4
Views
1,182
Hello, has anyone ever been caught in this situation? You have redundant CPUs, fieldbus is PROFINET, there are some devices which don't have the...
Replies
0
Views
515
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
Replies
4
Views
1,506
I am trying to load a .mer via USB to a PV+, when doing so I received an error that its not compatible. Using Dustin's little gem (thank you!)...
Replies
8
Views
1,444
Back
Top Bottom