Compact GuardLogix to Citect 8.2 ABCLX Issue

Newbie2016

Member
Join Date
Oct 2016
Location
Australia
Posts
7
Hi I am having comms issues between Citect 8.2 and Compact Guardlogix.

2023-07-14 07:50:54.788 +10:00 [ERROR] [CORE ] [0x114c] [IOServer ] [(GLOBAL) ] [ErrorLog() ] [errlog.cpp ] [266 ] Error: Channel offline, cannot talk UINIT 0015 PORT1_BOARD1 IODev Error_in_CMD-3 16 Generic 000021 Driver 536870934 (0x20000016)
2023-07-14 07:51:09.979 +10:00 [TRACE] [CORE ] [0x114c] [IOServer ] [(GLOBAL) ] [InitChannel() ] [plc_drv.cpp ] [1272] Channel PORT1_BOARD1 is Online


I am testing with one tag and the ABCLXDriver (v5.00.04) is saying the tag is good and successfully subscribed to. However I am getting #BAD on graphics.
 
Did you solve this issue, I'm having the exact same problem?


For the CLX driver, always check that the Tags in Citect can be found in the PLC


If there is a Tag address in Citect that is not in the PLC, random comms errors can occur - some graphics might be ok, some will say bad.
 

Similar Topics

gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
Replies
0
Views
118
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
303
Im trying to use a MSG instruction to get the serial numbers of all addon cards and display the serials on a HMI interface. I have the logic done...
Replies
2
Views
571
Hi all, we have a 1768 compactlogix 5345s safety controller firmware 20.14. it is randomly giving a major fault and a minor fault. the minor...
Replies
7
Views
1,425
I have an installation with a Compact GuardLogix 5380 CPU [5069-L306ERS2] that is experiencing a strange issue I have never encountered before...
Replies
15
Views
2,803
Back
Top Bottom