Hi,

I have the following setup:

4-20mA sensor -> PLC Input module

What I would like to do is have a primary signal and power cable, and a redundant signal and power cable.

With the power cable I could connect into the same terminals without concern, what I am unsure of is if there is an issue passing the 4-20mA current down two cables and terminating them on the same input terminal?

I would terminate the cable shields at the same earth terminal too.

Thanks
 
Hi,

I have the following setup:

4-20mA sensor -> PLC Input module

What I would like to do is have a primary signal and power cable, and a redundant signal and power cable.

With the power cable I could connect into the same terminals without concern, what I am unsure of is if there is an issue passing the 4-20mA current down two cables and terminating them on the same input terminal?

I would terminate the cable shields at the same earth terminal too.

Thanks

Is that really going to solve any problems, if the primary power cable gets shorted then so does the secondary by virtue of the fact they are paralleled ?
 
Hi,

I have the following setup:

4-20mA sensor -> PLC Input module

What I would like to do is have a primary signal and power cable, and a redundant signal and power cable.

With the power cable I could connect into the same terminals without concern, what I am unsure of is if there is an issue passing the 4-20mA current down two cables and terminating them on the same input terminal?

I would terminate the cable shields at the same earth terminal too.

Thanks

Do your instruments have space for two glands?
 
I see the point about shorted cables, yes it has space for two glands.

just to be clear, is this single instrument, single PLC input ?

You can sort the issue easily with Diodes/Fusing on the power, same problem with the analogues if you did connect them like that though.
 
If it's because your concerned about a cable "Break", just add in the plc program the ability to issue an "ALARM" event if reading would drop below 4 ma. This would be a sign that maybe the cable has broke.

If you have to have redundancy then add another sensor and use another channel then monitor both channels.
 
If it's because your concerned about a cable "Break", just add in the plc program the ability to issue an "ALARM" event if reading would drop below 4 ma. This would be a sign that maybe the cable has broke.

If you have to have redundancy then add another sensor and use another channel then monitor both channels.

My concern is data integrity not cable break detection. Therefore I need to ensure I have a redundant signal. The sensor goes into a clevis arrangement so it is not as simple as just adding another sensor. Hence why I am looking at the cabling options.

thanks
 
Just 'electrically' parallel the conductors/cables.


A 4-20mA loop has a single conductor between the power supply to the the transmitter to the receiver input and back to the power supply.



If you install cables with 2 conductors and connect both conductors to the same point in the loop, you have done have achieved "conductor redundancy". Or you could use separate conductor/cables.
 
Just 'electrically' parallel the conductors/cables.


A 4-20mA loop has a single conductor between the power supply to the the transmitter to the receiver input and back to the power supply.



If you install cables with 2 conductors and connect both conductors to the same point in the loop, you have done have achieved "conductor redundancy". Or you could use separate conductor/cables.

In this setup would creating a short in either set of cabling not induce a short the whole system?

I could put fuses/diodes at one end of the cables but not the other very easily.
 
My concern is data integrity not cable break detection.
?
What do you mean by "data integrity" ??
It sounds as if you want to have a better failure tolerance.

Exactly what kind of measurement is it ?
If this is a Pt100 or similar that is in a pocket or tube, then you can investigate if you can have 2 Pt100 sensors in the same pocket or tube. Then connect each Pt100 via separate cables to separate PLC inputs.
If measuring static pressure, you could have a tube with 2 attachment points for pressure transmitters.
Etc..
 
a short circuit from where to where?

For example if you have two cables, and one gets damaged causing a short between say the 4-20mA and +VDC conductor. This will also be present on the second cable as they are essentially connected at the terminals at either end.

Therefore without putting fuses/diodes at the terminations at both ends, if one cable becomes damaged the second cable won't be of any use anyway?
 
For example if you have two cables, and one gets damaged causing a short between say the 4-20mA and +VDC conductor. This will also be present on the second cable as they are essentially connected at the terminals at either end.

Therefore without putting fuses/diodes at the terminations at both ends, if one cable becomes damaged the second cable won't be of any use anyway?

I would assume a true redundant system would have a different input (different input card or rack). Landing to the same input seems more problematic than anything else.
 

Similar Topics

Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
576
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
Replies
13
Views
703
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
Replies
3
Views
281
Out of interest, I'd like some thoughts on what would be considered best practice with regards to a 2-position turntable control scheme (see...
Replies
17
Views
1,230
Hello colleagues Anybody knows, what could be the best or a better option to bring with you when you are in service at factory to connect via...
Replies
1
Views
285
Back
Top Bottom