xcyong89
Member
Hi All,
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Special Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Special Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance