Why AMIo800 Analog input module's I/O LED is Lighting up Red?
Checked module connections, 4-20ma wires etc but this light is continuously Lighting up and auto batching via VFD is not working.
 
This can be for a number of reasons, and sometimes it's not a problem, but depends on the configuration you have setup. The I/O LED typically is telling you there is a sensor issue. If you have channels enabled but not hooked up, it will light up. If you have it configured for 0-10V range, but have 24V on the signal (expecting 4-20mA), then this would also indicate an error as the value is out of range. If in 4-20mA range, the sensor could be outside of the range.

My guess, and is common if this is a first time setup is that you wired the 4-20mA sensor up to this using the Ic and 0v terminals, but the sensor receives power from the Iv terminal, so typically you need to jumper the Ic and Iv terminals somehow.

1712907776163.png

Check this document for more information. Modicon X80 - Analog input/output modules, User manual | Schneider Electric
 

Similar Topics

Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
34
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
129
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
141
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,208
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
285
Back
Top Bottom