Alan Bradley Messaging

jlreid17

Member
Join Date
Oct 2008
Location
Bristol
Posts
26
Is it possible to write a message from a SLC 500/5 to a micrologix 1100.

In the MSG setup screen I've checked the IP address and everything looks ok.

I'am getting an error
Connection not completed before user-specified timeout

The ethernet cable is ok

Any comment's welcome

Many Thanks

Jon
 
When you post questions about configurable instructions like the MSG instruction, it helps a great deal to post the details themselves, rather than your assessment of the details. In this case the actual IP addresses and the IP configurations of both the SLC-5/05 and the MicroLogix 1100 would be great.

The SLC-5/05 has the ability to communicate both using the older A-B Ethernet protocol, called CSPv4, and the new EtherNet/IP protocol that the MicroLogix 1100 uses.

When you configure a message to a MicroLogix 1100 (or a ControlLogix, for that matter), you must use the "Multi-Hop" configuration in the MSG instruction setup. When the target is a ControlLogix you can specify the Slot number of the controller. When the target is a MicroLogix, set the slot number value to 0.

Your SLC-5/05 also has to be of a firmware revision that supports the newer protocol. If the SLC-5/05 has the 10/100 Mb/s Ethernet port, it definitely also supports EtherNet/IP. Older 10 Mb/s only controllers need to have their firmware checked; I think that EtherNet/IP was added about 10 years ago in OS501 FRN 5, but I'd have to verify that.
 
Last edited:

Similar Topics

I have had to reload all of my software on my laptop today as the graphics card died. So, I have spent about the entire day reloading/registering...
Replies
53
Views
21,479
With Mitsubishi I can use a D file to both read to and from a timer. I have tried to do same with Alan Bradley but I can read timer with ACC and...
Replies
5
Views
3,025
S
Hi all, I am a new member and I found this website is very useful. I do have a question on Alan Bradley PLC 5 and need some assitant. How do I...
Replies
10
Views
4,807
hello everyone i am P.L.c new commer for instance and i hear about a brand name alan bradly, i spoke to my plc trainer and he didn't told me why...
Replies
30
Views
6,739
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
0
Views
16
Back
Top Bottom