Alan Bradley Messaging

jlreid17

Member
Join Date
Oct 2008
Location
Bristol
Posts
26
Is it possible to write a message from a SLC 500/5 to a micrologix 1100.

In the MSG setup screen I've checked the IP address and everything looks ok.

I'am getting an error
Connection not completed before user-specified timeout

The ethernet cable is ok

Any comment's welcome

Many Thanks

Jon
 
When you post questions about configurable instructions like the MSG instruction, it helps a great deal to post the details themselves, rather than your assessment of the details. In this case the actual IP addresses and the IP configurations of both the SLC-5/05 and the MicroLogix 1100 would be great.

The SLC-5/05 has the ability to communicate both using the older A-B Ethernet protocol, called CSPv4, and the new EtherNet/IP protocol that the MicroLogix 1100 uses.

When you configure a message to a MicroLogix 1100 (or a ControlLogix, for that matter), you must use the "Multi-Hop" configuration in the MSG instruction setup. When the target is a ControlLogix you can specify the Slot number of the controller. When the target is a MicroLogix, set the slot number value to 0.

Your SLC-5/05 also has to be of a firmware revision that supports the newer protocol. If the SLC-5/05 has the 10/100 Mb/s Ethernet port, it definitely also supports EtherNet/IP. Older 10 Mb/s only controllers need to have their firmware checked; I think that EtherNet/IP was added about 10 years ago in OS501 FRN 5, but I'd have to verify that.
 
Last edited:

Similar Topics

I have had to reload all of my software on my laptop today as the graphics card died. So, I have spent about the entire day reloading/registering...
Replies
53
Views
21,473
With Mitsubishi I can use a D file to both read to and from a timer. I have tried to do same with Alan Bradley but I can read timer with ACC and...
Replies
5
Views
3,024
S
Hi all, I am a new member and I found this website is very useful. I do have a question on Alan Bradley PLC 5 and need some assitant. How do I...
Replies
10
Views
4,803
hello everyone i am P.L.c new commer for instance and i hear about a brand name alan bradly, i spoke to my plc trainer and he didn't told me why...
Replies
30
Views
6,737
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
404
Back
Top Bottom