also dont forget about the SinecPni-V1.0.0.1 tool from siemens. It has saved my butt a few times when doing remote installations. I cant seem to figure out when the siemens plc actually auto configures the devices after download....I think it has to do with the topology layout (if it isnt 100% correct then it doesnt send the config). But I have seen this also happen with certain io devices other than siemens.... Then I just use the sinec tool and give profinet name and the plc will send the config as setup in tia portal