Hi All,

I've probably programmed hundreds of 1794-IE8's over the years. The panel builder I'm working with has installed thousands of these so I am reasonably sure that they wired them properly. Anyway, yesterday I was checking out a panel with 5 of these and all of them exhibited exactly the same problem.

I scaled the inputs programmatically to report 0 at 4ma and 30840 at 20ma. Every single input gave an offset of about 600 counts so instead of 0 input reported 600 at 4ma and 31440 at 20ma.

All of the modules are configured for 4-20ma and I DID NOT check out the wiring, perhaps I should have...

Anyone ever encounter this?

Thanks!

Yosi
 
I've seen two Flex I/O racks in noisy panels get flaky. Analog inputs and outputs would flatline and hold whatever value was happening at the time. Discrete I/O remained fine. A power cycle would clear that for a few hours or a few weeks. Turned out the Flex base ground tabs didn't pierce the oxide layer on the aluminum DIN rail. With a module pulled you can see one hole for panel mounting instead of rail mounting is grounding. None had continuity to the rail. A change to steel rail remedied the problem.
 
Last edited:

Similar Topics

Dear Members; We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when...
Replies
4
Views
1,869
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
Replies
8
Views
3,014
I am trying to scale an analog input for 4-20ma. Rockwell's website says that 0-30840 are the proper numbers. But the unscaled input raw is...
Replies
4
Views
1,899
Hello, I would like to install a 1.25k-ohm potentiometer to a 1794-IE8. All I have is a 24VDC source. I noticed that the input ranges from...
Replies
8
Views
2,112
Hi, I am using an Analog Input Module - 1794/IE8 My Analog Input Module is configured for 0-20mA Unscaled Max = 31208 Unscaled Min = 6241.6...
Replies
4
Views
7,071
Back
Top Bottom