Scaling 1794-ie8 in L75 processor

Boo

Member
Join Date
Feb 2020
Location
mo
Posts
3
I am trying to scale an analog input for 4-20ma. Rockwell's website says that 0-30840 are the proper numbers. But the unscaled input raw is already 32738. When I scale the raw max at the 30840 I get an out_pv of 106.15 which I know is not the current temp.
 
I suggest you post this in the Live Q&A as most do not read this area
Edit: 32768 is -0 as 32767 is max for 16 bit word you need to read it as an integer so you get negative values
32767 = +0 32768 = -0.
 
Last edited:
Yes it does equal 21 ma which I have learned is the default alarm condition for the Rosemount 644 transmitter that is connected to this card. The input raw was coming in at the 21ma which signaled that the transmitter was unhappy. I rescaled the input and then cycled the power. It is reading correctly now.
thank you all for your input. I have referenced this site for years and finally decided to become a member. The knowledge base here is fantastic.
 

Similar Topics

Hi, I am using an Analog Input Module - 1794/IE8 My Analog Input Module is configured for 0-20mA Unscaled Max = 31208 Unscaled Min = 6241.6...
Replies
4
Views
7,071
Hy Guys, I am doing scaling AB-Flex Analog Input 1794-IE8 with RsLogix-5000. I do scaling by 2 defferent method. The 1st-one I use direct Current...
Replies
0
Views
1,731
Hey guys, I'm reading in analog values from 1794-IE8 flex IO card to my PLC-5/40 using BTR instructions. Now, I'm doing my scaling in wonderware...
Replies
6
Views
9,901
Just commissioned two new skids for a customer. Each has a 1794 chassis over Ethernet back to an L81. The second module of each chassis is a...
Replies
8
Views
2,410
Hello. Wanted to ask you seasoned vets out there about a scaling issue I'm having. Controller migration. A 1771 IFE 0-5VDC analog signal...
Replies
3
Views
2,542
Back
Top Bottom