Hi , i have problem to configure redundancy of two plc , i have set into both plc the redundancy function and now i have PLC 1 with PRIMARY and the PLC 2 with DISQ message , in the rslink app i got fault that eth/ip module is incompatible with following error :

Incompatible : class 1 connections detected in partners not configured for ip address switching . the partners must be configured for IP swapping to support class 1 connections.

thanks :site:
 
I would recommend that you follow the Redundancy manual exactly because based on your description, you did not.
1756-UM015 for 5580 controllers or 1756-UM535 for 5570 controllers.

First, to control I/O (Class 1 connection mentioned) you must set both Ethernet modules to the same IP address. One will pick up IP+1 automatically.
Second, all firmware revisions for ALL modules in the redundancy chassis MUST be form the redundancy bundle, you can't use a random versions.
Then you do not load program to the secondary chassis. Code will be automatically crossloaded.
Lastly, for I/O and consumed tags you must use multicast I/O. Unicast is not supported with Redundancy.
 

Similar Topics

Hi All, I am trying to synch the primary with secondary, which apparently was disqualified due to Watchdog error. I am getting the following...
Replies
0
Views
934
Hello, My 1756-RM2/A Redundancy Module keeps entering the Disqualified module for half an hour or so, and then switches to Synchronized for like...
Replies
4
Views
6,501
Dear Colleagues, Now I'm testing Rockwell-based control system that has been stored for 8 years. Have some major issue, that have not met before...
Replies
0
Views
1,198
Hi Guys, Which version of RMCT that compatible with 1756-RM2 ver 20.017? I had RMCT ver 8.2.1.0 but when i try to configure 1756-RM2 there is a...
Replies
9
Views
9,496
Hello Guys, I had a problem with 1756-RM2/A. In my RS Linx (ver 3.51) It is shown as a mark question with red X sign that keep showing on and...
Replies
0
Views
1,974
Back
Top Bottom