Hi,

i'm working with a differential pressure transmitter yokogawa EJA130E and have problems to connect it to a Schneider analog module TM3AI4.

G-SE-0030427.2.gif-high.gif


I already try to wire it like the manual, also try to do a loop with the power supply and the transmitter doesnt turn on, the display remains blank.

2-wire-analog-input-wiring-external-supply.png


When i connect the transmitter directly to the power supply, the transmitter turn on.

Its my first project so i'm still a newbie, i'll appreciate any help.

Thanks
 
As the TM3AI4 is both voltage and current input, you need to configure the card in Machine Expert for 4-20mA. Its default is likely voltage input, which is high input impedance so the loop instrument won't work.

You'll need to wire the sensor loop powered like your second image if it's a 2 wire sensor.
 
Like this. You set the input for 4-20mA if you want the device to take care of low level and wire break alarms, you use 0-20mA if you want more control. Scale the 4-20mA to Real World values. I prefer my own scaling routine, but your PLC will almost certainly have a built in one.

4-20 Connection.JPG
 

Similar Topics

I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
4
Views
125
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
Replies
0
Views
151
Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
Replies
0
Views
92
Hey guys, the scenario is: I have already completed the drawing package for my system utilizing an A-B 440R-N23126 (Minotaur) safety relay. SoS...
Replies
0
Views
171
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
Replies
0
Views
124
Back
Top Bottom