Hi,

I have installed the WIKA A-10 to obtain the water level signal, and so far, it has been working fine without any problems. Let's see how it performs in the long run.
 
Problem: the range of the pressure transmitter is quite high considering that the actual level range is only 1 meter of water. Page 2 of the Wika A-10 spec sheet at this link
https://webapps.wika.com/apps/literature/pdf/F015_A10_0309.pdf
shows the lowest available pressure range as 0-15PSIG or approx 10.5 meters water column.

So you're measuring the 1m (wc) of hydrostatic (plus any hydrodynamic pressure from the agitator) with a 10.5m (wc) range using only ~10% of the range of the transmitter.

Maybe there's another model Wika that has a lower range? Pressures in this range are frequently measured with a DP transmitter.

Any pressure transmitter should be isolated from the hot liquid with a dead-headed impulse tube. Being dead-headed, with no flow through it, it will drop a lot of heat and keep the transmitter in a survivable temperature range.
 
Problem: the range of the pressure transmitter is quite high considering that the actual level range is only 1 meter of water. Page 2 of the Wika A-10 spec sheet at this link
https://webapps.wika.com/apps/literature/pdf/F015_A10_0309.pdf
shows the lowest available pressure range as 0-15PSIG or approx 10.5 meters water column.

So you're measuring the 1m (wc) of hydrostatic (plus any hydrodynamic pressure from the agitator) with a 10.5m (wc) range using only ~10% of the range of the transmitter.

Maybe there's another model Wika that has a lower range? Pressures in this range are frequently measured with a DP transmitter.

Any pressure transmitter should be isolated from the hot liquid with a dead-headed impulse tube. Being dead-headed, with no flow through it, it will drop a lot of heat and keep the transmitter in a survivable temperature range.
Hi;

I have installed Wika A-10, with range 0-100mbar.
 

Similar Topics

I'm having some difficulty figuring out when an AC line filter would be appropriate for an application. What exactly is being filtered, the...
Replies
2
Views
2,392
Hello experts, can you suggest me what would be appropriate motor protection switch for the following motor (used on a valve drive): 3 phase...
Replies
2
Views
2,012
Hello, I trying to determine if the use of a For/Next Loop is appropriate for my application. 1.) The code in question will check the value of...
Replies
9
Views
2,011
I'm converting 3 plc 5's to L72s. The first was converted last year using version 20. I used version 20 for this year's project, and had planned...
Replies
11
Views
5,491
Hey everyone. I need just about 10 feet of twisted pair shielded cable for a 4-20mA sensor that will be connected to a Koyo Click PLC. I have...
Replies
1
Views
1,752
Back
Top Bottom