I have a job with two EZ-Zone Ethernet/IP Controllers connected to a CompactLogix L18ERM. I've followed the documentation I could find in setting up the input/output assemblies for Implicit messaging, setting up UDTs, and copying from the raw assembly to the UDT.

I can't find any ladder logic examples anywhere for this. I realize most of it doesn't really require it since it's just writing and reading parameters, but what about enabling/disabling remotely? Is that even possible?
 
Is that even possible?
Yes. it is possible. I have been using Modbus TCP rather than Ethernet IP, but the technique should be the same.

For example, look at the EZ-Zone PM PID manual, page 39 in the "Control Loop Menu" section for the parameter "Control Mode". Write a value of 10 to that parameter to put the controller into auto mode. Write a value of 62 to turn the control loop of or 54 to put it into manual mode.
 
Yes. it is possible. I have been using Modbus TCP rather than Ethernet IP, but the technique should be the same.

For example, look at the EZ-Zone PM PID manual, page 39 in the "Control Loop Menu" section for the parameter "Control Mode". Write a value of 10 to that parameter to put the controller into auto mode. Write a value of 62 to turn the control loop of or 54 to put it into manual mode.

Thanks. I saw those numbers in the manual but I couldn't find an explanation as to what they were.
 

Similar Topics

I am tasked with connecting multiple Watlow EZ-Zone PM controllers to a Watlow EZ-Zone RUI/Gateway unit. They show up to 16 controllers connected...
Replies
5
Views
2,877
Hello everybody, I want collect data from EZ-ZONE PM (PM6C2CH-AAAAAAA). I saw in datasheet it only support standard IEA-485. And datasheet donot...
Replies
2
Views
2,519
I'm a newbie who started a job as a repair tech recently. I've had plenty of luck with ABBs, Allen Bradleys, and a few others, but I can't seem to...
Replies
1
Views
191
Good Eve Gentlemen, We had this cold room which was converted to hot room before I joined this work. Everthing was fine until a month ago, they...
Replies
9
Views
2,140
My system has an Allen Bradley PLC, Red Lion CR3000 HMI, and a Watlow F4T controller. I am able to read registers from the Watlow F4T via Modbus...
Replies
0
Views
1,658
Back
Top Bottom