Our MechE is asking, it is for a product I don't deal with. My first reaction was sure why not? it is like 1/8Amp at 480VAC. Then he was like, well is there anything in UL508 that says you aren't allowed to have an unbalanced 3pH load?

I can't find anything about this subject in the standard, but that doesn't mean it isn't there. :unsure:

We have always used 3pH power supplies on that product, but we are having issues sourcing them, so they want to switch to a single phase.
 
It’s fine so long as
- the power supply is 508 listed
- you use proper branch circuit protection
- use properly sized/ rated conductors
 
I constantly use 3 phase 480 to 24VDC power supplies - usually 90W, but 60W isn't much different. Just make sure they are rated for the voltage input, they are UL listed, and you are using the right sized conductors.

They won't unbalance your load any more than a transformer will.
 
With such a small load you will not notice an imbalance great enough to effect anything. If there are other single phase loads it is common to even the single phase loads out between different legs. If this is the only one I would not worry.

Note: I am not aware of a section in UL that covers this, but does not mean there is not one. Some plants with 240V and a high leg have no choice but to put all single phase loads on the two phases available
 
You cant use a control power transformer in a 508 panel?
No he was saying if I logically couldn't connect a DC power supply to 2 legs, then it would follow that you couldn't do that with a transformer either.

Which is obviously not true.


I shall admit, my question was dumb but my MechE's question got me questioning my own reality lol

I used to supply transforms and Power supples from 2 legs all the time, but that wasn't at a 508 Shop.
 
If anyone were concerned, control power transformers would be forbidden…

Fuggedaboudit…


Single phase in VFD's, most smaller robot controllers are single phase that control all 6 axis', almost all heaters.....


Quite a few things can be single phase line voltage - it's up to us to make sure there isn't a phase imbalance by wiring them all A to B.
 

Similar Topics

Any suggestions on how to repair the power supply GT27-10PWD in the display (GT2508)? Any documentation or place that fixes it? Thanks in...
Replies
2
Views
653
Hi please need your help, can I install the Proximity Probe 21508-02-12-05-02 Bentley Nevada on the drive 1442-DR-5850 from Allen-Bradley using...
Replies
2
Views
2,159
We are becoming certified as a UL508A panel shop. Of course, one of the requirements is a torque screwdriver calibrated yearly. Just reaching...
Replies
9
Views
3,321
Hi all, We are working on an offshore installation, to be deployed in UK waters. We had the system surveyed during a FAT by DnVGL and thought...
Replies
4
Views
1,722
All, What type of naming convention do you use for labeling the locations of each area in your cabinet? Is it arbitrary or based off of where...
Replies
1
Views
1,143
Back
Top Bottom