Got a trouble call from a customer this AM that one of the compressor systems is getting its setpoint overwritten and mode (local/remote) constantly changed. The SP comes from another CLX and is rock-steady in that program. Disabling the MSG instruction causes the compressor program to get a 0 value, which we are unable to overwrite. We unplugged the local HMI (serial cable) to the compressor PLC and it did not help, so we assume there is a MSG write instruction out there writing to this PLC, but as we all know, this is the problem with MSG instructions. I'd be curious if anyone has any solutions in tracing MSG writes.
 
That was my only thought at first. I got lucky and went to the web page of the ethernet card (in this case a NET-ENI) and happened to see another incoming connection. Turns out one of the automation guys who was in last night fired up his test PLC and left it on, which happened to be an older copy of a program that writes to that compressor.
 
For reasons such as this, we have a policy to NEVER do MSG Writes to other PLCs....always read the info you need.
 
As does this customer, but there are several instances where they still exist and we are trying to help them convert all of them.
 

Similar Topics

I am adding an inspection system on an existing conveyor. The idea is that if the bin contains a defect it will fail inspection and once it...
Replies
9
Views
2,161
Team, I have the need to gather the run down info from the copco controller to my PLC. I have an Allen Bradley PLC running v28. Has anyone here...
Replies
7
Views
3,244
I am attempting to reject a bottle If the label fails. The rejection works fine at normal line speed but at low speed the rejector fires (air...
Replies
35
Views
1,148
Is it possible to gather OPC data through a 1783-NATR? Searching around, it sounds like OPC data might be blocked by any NAT... Is there any work...
Replies
2
Views
247
Hi All. I have a very specific question about tracking using an encoder and bitshift register. We would like to use a Compact or Control Logix PLC...
Replies
40
Views
1,730
Back
Top Bottom