I have a device that is communicating to ControlLogix L83E. During apply of online edits to plc, the communication to the device is increasing 4-7 times (from 100ms to 400-700ms) resulting into a comms fault error. Pls advise if there is a controller flag I can use to bypass the comms fault during online edits download.
It's an issue of inconvenience, every time when doing online edits, you have to reset the fault.
 
Hi,
We would need to know the network architecture and the number of connections the L83E has open concurrently.
L83 is pretty beefy, hard to imagine a comms issue that's not originating somewhere else.
 
Can you limit the number of sockets used by your application? I believe you can limit the number of sockets in Linx. You certainly could for the SLC500s.
 

Similar Topics

Basically I have created a bunch of local tags, is it possible to convert all of these to a global tag? Or would I need to re-add everything all...
Replies
5
Views
1,199
I'm working on a project, adding a couple large machine components to an existing Control Logix L71S. The original program was written in v20. I...
Replies
4
Views
1,018
Hi All, Can I get help with the following Invalid Input Size Fault displayed in Studio 5000. Allen Bradley: Studio 5000 V33 CompactLogix...
Replies
1
Views
1,434
Hi guys. I'm trying to display the controller firmware revision number OR the logix designer version number on my panelview plus 6 HMI. So I think...
Replies
10
Views
1,781
Hello everyone, This is my first post in the forum, although I have been here more times that I can count for various questions I have had from...
Replies
1
Views
1,207
Back
Top Bottom