You have a 16A rated soft starter.

You have a 1/3HP 480V motor, the FLA is likely in the area of 0.9A.

So if the motor is unloaded the current is likely even lower than that.

The SMC-3 (and most soft starters) need to see a rise to a minimum of 100% of their programmed motor current to pull in the bypass contactor, otherwise they will shut assuming the motor is not connected. In the case of a 16A rated unit, the motor current is not adjustable to a value of less than 5.3A. So even at Locked Rotor Current, that little tiny motor would not pull enough current to make the soft starter work.

By the way, you cannot program the OL protection to protect that motor either. You needed to use the smallest version of the SMC-3, the 3A unit, because the motor current can be set down to 1A (which may be as close as you can get with a soft starter).
 
You have a 16A rated soft starter.

You have a 1/3HP 480V motor, the FLA is likely in the area of 0.9A.

So if the motor is unloaded the current is likely even lower than that.

The SMC-3 (and most soft starters) need to see a rise to a minimum of 100% of their programmed motor current to pull in the bypass contactor, otherwise they will shut assuming the motor is not connected. In the case of a 16A rated unit, the motor current is not adjustable to a value of less than 5.3A. So even at Locked Rotor Current, that little tiny motor would not pull enough current to make the soft starter work.

By the way, you cannot program the OL protection to protect that motor either. You needed to use the smallest version of the SMC-3, the 3A unit, because the motor current can be set down to 1A (which may be as close as you can get with a soft starter).


I believe you are correct. We hooked up a 2HP motor to it and it works correctly.
 

Similar Topics

Does a solid state soft starter have a DC Buss / DC Buss voltage like a VFD does?
Replies
1
Views
254
Haven't done much with soft starts, more-so VFDs' in my time. Looking at replacing 3 x 37KW (415 V 50 Hz) star-delta starters with soft starters...
Replies
11
Views
2,876
Is there a way to get the fault history from a SIRIUS 3RW4456 Soft Start through the HMI keypad? I've been through the manual but it is pretty...
Replies
0
Views
746
We are going to be using a SIRUS 3RW5545 Soft Start to control a 480V, 150HP fan. Looking for some recommendations for parameters to use with this...
Replies
0
Views
850
Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
Replies
16
Views
4,248
Back
Top Bottom