SLC 500 5/03 PID block- PV not wanting to be read by the PID block

jakeparsons03

Member
Join Date
Jun 2017
Location
Indiana
Posts
78
Hello,

I have a PID block in my program controlling pump speed in order to get a correct Differential pressure.

The way I have it set up is the current DP is reading into the PV on the PID block. The DP is accurate and moving. The issue is, when I go into my PID setup screen the PV always reads 0. Which as you could probably understand is really throwing everything off. I do have a UL flag thrown which I am also trying to figure out but I don't think that should have anything to do with the PV.
 
Alright so I think I figured something out. I put in a new input into the PV and it took it. I:18.0. So can the PV only be an input value? It can't be on an N Table or is there other tables that will work?
 
Figured it out. My pv was scaled for the actual pressure. I figured that if my pv and my sp were both scaled the same it wouldn't matter but apparenlty the equation doesn't work for that small of numbers. Once i scaled both to 0 to 16383 it worked.
 

Similar Topics

How can I test some PID code I have written for a SLC-500 in RSLogix500, without having an actual processor to test on. I have used Emulate500 to...
Replies
3
Views
1,837
I have a PID in a SLC 500 that does not function as it should. Have deleted it remade it and still have a problem also moved it up and down in the...
Replies
13
Views
2,761
I am new to the SLC 500 platform and am hoping that someone can give me some hints on how to do PID and ramp/soak with the SLC 500 and perhaps...
Replies
11
Views
6,661
Please Help me to make this PID working. I had done PID according to AB manual but it is not working. when I am manully changing the CV at setup...
Replies
6
Views
7,572
Hi All, I want to know There is some relationship between SLC500 or PLC5, Controllogix watchdog time and PID loop update time. Does it need to set...
Replies
2
Views
5,271
Back
Top Bottom