SLC 5/05 Major error wont clear.

dsking

Member
Join Date
Dec 2008
Location
ontario
Posts
66
Hi there,
I have SLC 5/05 PLC with one one expansion I/O rack.
The fault line is not on. However in the processor status debug page it lists this error "Remote power failure of an expansion I/O rack occurred."
The power to the expansion rack is on and the I/O are workin fine. The error cannot be cleared. I'm not sure why and was wondering if one of you great minds up there can point me in the right direction.
Thanks.
 
Maybe, from AB's knowledgebase

3
8247 - SLC Processor: Error Code 21H
Access Level: Everyone
Date Created: 02/09/2007 03:37 PM
Last Updated: 12/16/2010 11:36 PM


I am generating error code 21H in S:6 of my slc 500 series processor.

What does this error code mean?

Error code 21H indicates that one of the modules in the slc 500 chassis is faulting.

The exact description is "A remote power failure of an expansion I/O chassis has occurred.

The customer should download a blank program and force the program into run mode.

Adding one module at a time to the I/O and placing the program in run mode.
 
Just wondering if you have a Prosoft card in the mix? I had the same thing untill I removed the prosoft from ALL of the faulting units.
 
Hi there,
I have SLC 5/05 PLC with one one expansion I/O rack.
The fault [LED?] is not on. However in the processor status debug page it lists this error "Remote power failure of an expansion I/O rack occurred."
The power to the expansion rack is on and the I/O are workin fine. The error cannot be cleared. I'm not sure why and was wondering if one of you great minds up there can point me in the right direction.
Thanks.

If the Fault LED is OFF, then the fault is already cleared. What you are seeing is the last major error code. This is normal. It won't clear with the Clear Major Error button, because S:1/13 is not set. This is all intentional so you can have evidence of what the fault was long after clearing it and getting the machine running again.

If you want to make the fault "history" go away, put a zero in S:6 and S:54 manually (you must change the radix to edit S:54).

EDIT: no need to change the radix for S:6, you can enter the zero right there on the structured view...to clear S:54, change to decimal or some radix other than structured.

LastMajorErrorSLC.jpg
 
Last edited:
Wow!!!!!! thanks everybody.
OkiePC thanks, I succesifully cleared the fault history following the steps you suggested all. Greatly appreciated.
 

Similar Topics

Hi, We are having issues with an intermittent Major error code 21h. The plc can be running for varying amounts of time before faulting anything...
Replies
9
Views
1,897
Hi everyone, I hope you can really help me with this problem. First of all I have to said that I'm a begginer programmer. We have an AB SLC 500...
Replies
1
Views
1,882
I have an SLC 5/3 with an SLC 500 anaolg input module, 1746-NI4. Each time that i want to go online (with no inputs connected) the processor goes...
Replies
1
Views
1,494
I just had a SLC 5/05 fault on a major error. The error code was 20H which according to the manual says "A minor error bit is set at the end of...
Replies
9
Views
6,874
Have communications with processor, but won't read I/O config. Will Download to processor, but when you go to "RUN" it immediately faults to error...
Replies
4
Views
4,488
Back
Top Bottom