I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in diagnostics but the value always reads 0.

We are using another PLC analog output to test the AI so we know what is coming out and can measure it on the AI terminals. We have replaced the module with a spare and we have the same behaviour on that too.

Weirdly if we move the input to the AI on the cpu it reads as expected so this proves the test PLC output side of things. I've also tried several HW downloads with no effect.

One thing I've just thought of as I'm typing is to delete the module and re-add to the project to see if that helps.

Other than that does anyone have any ideas or spot the obvious mistake I'm missing?

TIA (Thanks in Advance!)
 
How is it wired? The SM1231 needs 24v connecting to the L and M terminals.

Other than that, I think a firmware mis-match would show an error when you download.

It's possible to turn off the input in the hardware setup or set conditions on when it is called. You can directly address it using the suffix ":p" (e.g rather than %IW15, it would be %IW15:p) to get around this.
 
It's possible to turn off the input in the hardware setup or set conditions on when it is called. You can directly address it using the suffix ":p" (e.g rather than %IW15, it would be %IW15:p) to get around this.

It's wired correctly. I've been playing around since I posted earlier and found channel 3 seems to work ok and I can address all channels via ":p" so it seems the like the channels need activating as you suggest.

Where can I find this option as I've gone through the HW config a few times and not noticed it?
 
Last edited:
I may be wrong about that, I don't have TIA in front of me so I can't check. I know you can disable channels on a 1500 and ET200 so I was assuming you can on a 1200.
 

Similar Topics

Hello Experts, I need your help about this issue of mine about my Siemens Analog Input Card SM331 having SF LED lit. I know this is system fault...
Replies
2
Views
4,496
Hi, I've been reading the contents of the forum for a while and finally decided to ask a particular question related to a project I'm currently...
Replies
9
Views
4,329
I am a student. I can program PLC using LAD language using digital IO. But, I want to program using analog IO also. We have analog IO module with...
Replies
2
Views
2,082
Hello I've got a signal from a potmeter ranging from 3v to 8v and a feedback from an actuator ranging from 0 to 10v. Ive tried to set up a...
Replies
1
Views
1,511
Hello guys, I need your help again. Haven't did anything with PLC for a long time, but now I have some little confusion. Equipement: Siemens...
Replies
18
Views
6,256
Back
Top Bottom