Hi guys,
So we had a network crash and the lines wouldn't start. This created a new project for me to add a selector switch and a pot to each conveyor drive to run them locally. Currently the drives are controlled via Ethernet and hardwired e-stops - this won't change.
The drive is wired from terminal 11 through the safety relay to terminal 1 & 7. Terminal 7 is programmed in the drive to use Ethernet as its source for both control and speed. So far, so good...
So I thought that I had it figured out, I added the switch and the pot, changed parameters 48 & 49 in the drive to look for the digital input and use the pot. But no go.
Do I need to change parameter 67 to 3? It's already set to 5.
Thanks!