Schneider Modicon M340 CanOpen error

david_n

Member
Join Date
Jun 2019
Location
Krakow
Posts
4
Hi,

I'm configuring the M340 controller with ATV320 inverters via Canopen. Everything was fine until today, when after starting the electrical cabinet, the CPU cannot communicate with the inverters. Nothing has been changed since yesterday not even touched.

Below are errors from the CPU and Canopen:

CPU:
https://pasteboard.co/6PwOb5TpPxKP.jpg

Canopen:
https://pasteboard.co/SZOAaTLiA6Lf.jpg

CPU is in RUN so I/O modules run normally.

Please help me solve the problem,

greetings
 
Last edited:
With the ATV320 this is normal behaviour after a power cycle.
In the slaves you need to specify what the master does to the slave (atv320) config at power up. By default it is set to reset, which is dumb.
Attached is picture showing the culprit settings in default.
In the picture I have already changed them

canopen.PNG
 

Similar Topics

Hello, I'm having a hard time understanding how to get a Modicon M340 to pull a Modbus address from an ABB Totalflow via Ethernet. I set up a port...
Replies
5
Views
1,185
Hi, Does anyone know if programming a Modicon M580 is basically the same format as an M340? Also do they use the same software package? Thanks...
Replies
2
Views
1,797
Hi all, im in urgent need of some help in programming a telemec modicon m340. If anybody can help i would greatly appreciate it. Cheers
Replies
5
Views
1,849
i make the program in plc m340 schneider and dump the program into it.but its indicate i/o problem.what is best way checking procedure:D
Replies
0
Views
2,846
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
Replies
4
Views
149
Back
Top Bottom