S7-300 Analog input module

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Dear experts,

I would like to ask what should I configure with this Analog Input Module 6ES7 331-7KB02-0AB0. I have a 0-10V DC Analog signal coming from a sensor. I will input this to the first channel of 6ES7 331-7KB02-0AB0. I found out that in the HW Config Pull-down using Simatic Manager menu under E (voltage), I could not see 0-10V but +/- 10V. What should i select???

Please help, maybe I have overlooked some parts.

Thanks,
Alex
 
You can configure your analogue input/output while configuring your hardware. There are 3 possible configurations for analogue inputs and outputs
+/- 10 V
0 to 10 V
0 to 5 V

Configure your hardware to 0 to 10 V
 