S7-1515-2 Output card losing output voltage

Tadicus

Member
Join Date
Feb 2018
Location
Livingston, MI
Posts
2
I have a Siemens 1515 controller with the configuration of cards (input, output, safety input, safety input, safety output). I am having an issue with the output card (6ES7522-1BH10-0AA0) losing voltage once connected to a load. We have it connected to our stack light and estop pushbutton light. We have the output on on the card and trace 24VDC when unwired from the lights. However, when we connect to the lights, the voltage drops anywhere to 3VDC-11VDC. The 0VDC are all tied together at terminal. We have also tried swapping out the base for the output card itself. Any help would be appreciated.
This is on a new commissioned system.
Thanks, Tad
 
This card has 16 channels with 2 groups of 8, each group has to get power of 24vdc.
First group ( CH0 - CH7) ,check 24 vdc in terminals 9 and 10.
Second group (CH8 - CH15), check 24 vdc in terminals 19 and 20.
 
Resolved!

Thank you for the follow-up. The card was swapped out with another and also didn't work. We found the wiring on 9 and 10 to be backwards. This caused a short circuit in the cards. Both cards have been tested against another known working PLC. Neither card worked but the one installed did.

Thanks, Tad


Two output cards later. Always check your wiring first.
 

Similar Topics

My company is commissioning a new machine and we're having a few issues with I/O Channel errors. My Italian colleague took a screen shot for me to...
Replies
6
Views
2,370
Hello, My client uses 6ES7 515-2AM01-0AB0 and on port X2 P1 they connected an external database in 192.168.1.xxx pool. The other ports X1 P1 /...
Replies
2
Views
1,981
Hi guys, Siemens PLC CPU 1515 2 PN display black out. We measured the input supply 24 vdc is available but CPU display is not showing...
Replies
0
Views
1,307
I am trying to control an ABB ACS800, with a RETA-02 com.card, over Profinet. But without any luck! :( The system i set up with a S7-1515-2PN...
Replies
1
Views
2,134
Just stumpled accross some tidbits of information about a new IPC in the shape of ET200SP/S7-1212SP. It is called S7-1515 SP PC Open Controller...
Replies
17
Views
13,376
Back
Top Bottom