Hello all,

I have set up a PID loop which works fine except it is a bit slow during the startup.
I wish that it would reach near the setpoint faster. What should I look into?

The PID controls the flow of a pump. I am happy after the startup, it is only the startup I want to improve.
It takes about 15sec to stabilize.
I noticed that if I make P larger and I smaller, then I get a faster response and big overshoot followed by a big undershoot. If I remove D then I get a huge oscillation until it stabilizes.

P=0.004
I=3.2
D=0.935

1.jpg
 
Only run the loop when the pump is running.

You could do this for instance by setting the loop to manual mode as you stop the pump. Now the output signal (speed for the pump) is locked.

When you start the pump, you keep the PID in manual mode for a set period of time (until the pump has had a chance to build up the pressure) then you switch it over to automatic.

PS. For tips on tuning, do you have a graph that shows the pressure like the one above but together with the output of the PID?

I assume your pump is run by a VFD. Check so that you don't have any large ramp up/down times setup in the VFD.
 
Last edited:

Similar Topics

how can i use pid+pwm to control brightness of the ac light
Replies
4
Views
2,261
Hello everyone, this is my tutorial for using PID function on S7-1200. Hope you guy like it. https://www.youtube.com/watch?v=INB6_7SqeOg
Replies
0
Views
1,643
Hello everyone, I'm new in using plc software. I want to set a parameter for my centrifugal pump using an i/p from PID block so that the range of...
Replies
0
Views
1,291
Hello, I changed controller type in RSLogix 500 from SLC 5/02 to MicroLogix 1200 and was given the ladder logic to update it for the new...
Replies
25
Views
4,847
Hello to all, We have to reload the program on our s7-1200. The program uses PID loops. Will, after reloading the program, be neccessary to...
Replies
0
Views
1,412
Back
Top Bottom