Not all drives have safe torque off, if yours doesn't you can disregard.
The drive can be configured to look at Modbus, Digital Inputs, or Both. Make sure it's not set to both.
As per my previous post, Reference 1 Source is the parameter you need to look at for sending a speed reference over modbus. Of course you also need to make sure that Reference 1 is selected, but generally it will be selected by default.
Ah thank you. I have set the drive to listen to both Digital Inputs and Modbus. So it might be that. Can't make changes at the moment but will certainly look at that when the load shedding ends.